Air Exhaust from the UPS Battery Building

10/18/2010 2:01 PM

I need to to know the amount of air required to flow thru the exhaust fan from the UPS battery building of size approximately 1,000 cubic feet (volume).

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#1

Re: Air exhaust from the UPS battery building

10/18/2010 2:08 PM

Information missing: battery array offgas rate, standby/discharge/charging.

Is there free air transfer already available? Will it thermosiphon?

Will your classmates not share their notes?

__________________
Semper Ubi Sub Ubi
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Air Exhaust from the UPS Battery Building

10/18/2010 4:07 PM

Rule #75. Is there 1 battery or 100 batteries in the alleged battery building?

Where do they come from.

Reply
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#3
In reply to #2

Re: Air Exhaust from the UPS Battery Building

10/18/2010 4:25 PM

I am simply assuming 1000 Ft3 of battery volume. Why not?

I sometimes see a homework question verbatim. While a sure way to get the CR4 lazy-student abuse, at least we have most of the data.

Perhaps schools need a class titled "How to paraphrase a homework question so CR4 members might help you without busting your chops - 101"

I feel the same as you; just plain old .

__________________
Semper Ubi Sub Ubi
Reply Score 1 for Off Topic
Anonymous Poster
#4
In reply to #3

Re: Air Exhaust from the UPS Battery Building

10/18/2010 6:13 PM

This is not the home work.

There are 60 Excide GNB 100G57 VRLA batteries for a 60 KVA, 2 Hour back up UPS. I looked into some documents in internet but didn't find concrete answer.

If you have expertise, please respond with helping attitude. Greatly appreciate.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#5

Re: Air Exhaust from the UPS Battery Building

10/18/2010 6:34 PM

I don't know what the number is.

It comes down to how often you will need to turn the air over in the room for proper ventilation. I'd use pusher fans.

If it turns out that the number is 3 times per hour, I trust that you will be able to perform the required math operations.

Reply
3
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Air Exhaust from the UPS Battery Building

10/18/2010 8:15 PM

The required number of air changes per hour (A) is given by the following formula:

0.045 x N x I = A
V

Where:
N = Number of cells in the battery
V = Volume of room in cubic metres
I = Charge rate in Amperes

This formula will give the number of air changes per hour required during boost charge conditions. On float charge (systems are on float charge for most of their service life), the amount of gas emitted is approximately 1.5% of that liberated whilst on boost charge and under most circumstances this will be dissipated by natural ventilation, and will not present a hazard. However, we recommend that the boost charge condition is allowed for at the design stage to ensure the appropriate decision on ventilation requirements is made.

Although Valve Regulated Lead-Acid Batteries require little ventilation under normal operating conditions, it is good practice to apply the formula to calculate the number of air changes required to achieve minimum risk under battery fault or failure conditions

__________________
The reports of my death are greatly exaggerated.
Reply Good Answer (Score 3)
Guru
Hobbies - DIY Welding - Don't Know What Made The Old Title Attractive... Popular Science - Weaponology - New Member United States - US - Statue of Liberty - 60 Year Member

Join Date: Apr 2009
Location: Yellowstone Valley, in Big Sky Country
Posts: 7425
Good Answers: 295
#7
In reply to #6

Re: Air Exhaust from the UPS Battery Building

10/19/2010 3:39 PM

All right, here we go: Feeling generous if not homework: trying for helpful attitude!

Formula in #6 is variant of the Document for Battery Rooms by Exide Technologies.

Q = 0.05 x N x I (meter3/hour) N= No of cells, I = charge current

More to ponder:

NFPA 76: Fan capacity should be 1 CFM per Sq Ft of floor space.

ASHRAE 62: 1 CFM per charging amp, no less than 6 changes per hour

IS:1332: Battery Room - 12 Air Changes per hour

__________________
Semper Ubi Sub Ubi
Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#8

Re: Air Exhaust from the UPS Battery Building

10/19/2010 7:21 PM

This is no definitive answer to the number of air exchange. I have seen it varying from a low number (2) to a high number (30). Here is some of the related standard reference:

(1) DNV-OS-D201, Article 304: For VRLA batteries over the UPS capacity 40 KVAh (yours is 60 x 2 = 120 KVAh), the minimum 30 changes per hour. However this requirement is during the deep charge of batteries.

(2) NFPA-1: Fire Code, Article 52.3.6: the air exchange rate not less than 1 ft3/min/floor area in square foot.

(3) EN 50272-2 has a formula (Q = 0,05 x n x Igas x Crt . 10-3 [m3/h]) in the article 8.2: Ventilation Requirement.

There is another recommendation from NFPA for vented batteries – 2 air change per hour.

I worked in an offshore project where the requirement for battery room was 10 air changes per hour; while in another similar project, the requirement was the complete room air change within two minutes (equivalent 30 air changes per hour).

The formula that TonyS suggested also can be followed.

The LEL (Lower Explosion Limit) of hydrogen is 4%. So, it is recommended that the limit shall be kept lower than 1% for better safety. So, you can find the maximum hydrogen evolution from the batteries during deep charge from the vendor, and calculate the requirement of the air change rate to limit the level to below 1%.

There are other important things about the battery room ventilation and they are:

(1) The equal amount of fresh air to be intake into the room, so that no significant negative pressure occurs in the room.

(2) The standby fan should be in place so that if one fails, the other one starts

(3) The air flow can be controlled; the air flow rate requires increase for case of hydrogen detection in the room

Here is some links that also may help you (you might have already seen them):

http://www.apcmedia.com/salestools/SADE-5TNQZQ_R2_EN.pdf

http://140.194.76.129/publications/armytm/tm5-691/c-7.pdf

http://www.cholarisk.com/Files/Risk%20Note%20on%20Explosion%20Risks%20in%20Battery%20Rooms.pdf

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)
Reply to Forum Thread 8 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Doorman (3); lyn (2); msamad (1); TonyS (1)