Motor Tripping Problem (Centrifugal Pump)

10/18/2010 2:00 PM

Hello guys,

Can you plz help me out in sorting out a tripping problem of Motor's of centrifugal pumps. It is as below...

We have 5 no of 30 kw pump motors, used to supply cooling water from cooling tower to our compressors. At at a time, we to run to 2 nos. Water flow required to cool compressors is more than enough to our requirement. Tripping is done by OLR when pumps are running normally. Also when we run two pumps, we can only run one pump by fully throttling there outlet valve and other one by reducing 50% or more. If we operate both in full throttle they tripped. Also impellers of 4 out 5 pumps have been changed with little different speccifications i.e. Impeller dia. reduced from 400 mm to 390 mm, but with 20% additional weight. There surface finish and aerodynamic is not as good as the previous one's. Does it have any impact on this tripping problem.

Power Ratings are as below:

Make Siemens

Max. KW Rating 30 kw

Max. Amp. Rating 52 Amp.

Voltage 400 Volt plus minus 20 (Actual Voltage is 440 Volt)

Power Factor 0.83 plus minus 0.02

Frequency 49.70 plus minus 0.5 (Actual Frequency 50)

RPM Around 1460 rpm

Pump Head 30 mtr. (more than enough we require)

If anyone can suggest solution to adress this problem???

__________________
Gurvir
Register to Reply
Pathfinder Tags: Tripping Problem
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Motor Tripping Problem (Centrifugal Pump)

10/18/2010 2:10 PM

If it is tripping on overload, that usually means it is over loaded! If you measure the current and it is higher than the FLA on the motor, then you are overloading the motor.

Does changing the pump impeller have an effect? ABSOLUTELY!!!

In centrifugal pumps, "load" is equal to flow. If you increase the flow, you increase the load on the motor. An engineer would (should) have selected the motor so that the BHP requirements of the pump, based on expected flow at expected head at expected pressure, is about 80% of the motor HP (I'm sorry, I don't know the metric equivalent of BHP). If your flow, head or pressure is different from what the original design was, there is no telling what you are demanding of that motor now.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Motor Tripping Problem (Centrifugal Pump)

10/18/2010 2:36 PM

Perhaps trim some more off the problem impellers so they are non-overloading regardless of where the pumps operate along their respective curves.

(The fewer pumps you run, the less ΔP in the piping. This moves the pump operation to the right on the curve. The flow increases more than the pressure decreases; hence the BHP increases and thus can overload the motor.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#3

Re: Motor Tripping Problem (Centrifugal Pump)

10/18/2010 4:32 PM

"Voltage 400 Volt plus minus 20 (Actual Voltage is 440 Volt)" Does this mean you are operating at 400V +- 20V and the motor is rated for 440V?

Is your phase to phase voltage and current balanced?

__________________
CRTL-Z
Register to Reply
Member

Join Date: Jan 2009
Location: India
Posts: 5
#4
In reply to #3

Re: Motor Tripping Problem (Centrifugal Pump)

10/18/2010 5:08 PM

Yea, thats right. Motor is rated for 440 Volt.

It was balanced (Phase current difference was 1 amp to 2 amp then) before. We did checked it and tripping was there at that time too. But now phase current difference is 5 amp to 6 amp. How could we overcome That???

__________________
Gurvir
Register to Reply
Guru

Join Date: Feb 2008
Location: Large hole formally occupied by furry woodland creature.
Posts: 3385
Good Answers: 97
#6
In reply to #4

Re: Motor Tripping Problem (Centrifugal Pump)

10/18/2010 5:32 PM

As JRaef mentioned in post#1, your motors are being overloaded, as a result of insufficient voltage.

__________________
CRTL-Z
Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#5

Re: Motor Tripping Problem (Centrifugal Pump)

10/18/2010 5:29 PM

I agree with everything else said here, but would add one more thing--get somebody out there with a (clamp on) ammeter and measure the current. Then you'll know for sure what is going on.

If it was happening on just one pump, I could suspect a defective motor starter/controller, the wrong overload heaters, or just overload heaters that have been in service for a long time and no longer work at the proper rating.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#7

Re: Motor Tripping Problem (Centrifugal Pump)

10/18/2010 11:07 PM

Are you having similar problems elsewhere on you system? If not I'd take a very close look at the supply to the 5 starters. It could be something as silly as a bad connection to the supply Dis board or MCC panel.
Whatever it is, it's common to them all.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Jun 2010
Posts: 2
#8

Re: Motor Tripping Problem (Centrifugal Pump)

10/18/2010 11:27 PM

if your pump head is more than required ,then also you face tripping problem,because if your pump is running under low head(with respect to design head) than flow will increase,naturally motor amp will increase and motor will tripp.

Register to Reply
Guru
Safety - ESD - New Member Popular Science - Cosmology - Amateur Astronomer Technical Fields - Technical Writing - Writer India - Member - Regular CR4 participant Engineering Fields - Optical Engineering - New Member

Join Date: Dec 2007
Location: 18 29 N 73 57E
Posts: 1390
Good Answers: 31
#9

Re: Motor Tripping Problem (Centrifugal Pump)

10/18/2010 11:47 PM

Keep the valves closed, while starting the pumps. Once the pumps start running at full speed, then only open the valves.

The problem will be solved.

Register to Reply
Active Contributor

Join Date: Aug 2010
Posts: 13
#10

Re: Motor Tripping Problem (Centrifugal Pump)

10/18/2010 11:53 PM

Check your pump curve (if you have one), it appears your operating point requires next size motor, which is 37kW.

Why not upgrade motor & not throttle pumps' discharge valve?

This exercise may require uprating the supply cable, starter contactors and O/L relay & it's settings.

Register to Reply
Active Contributor

Join Date: Sep 2010
Posts: 22
#11

Re: Motor Tripping Problem (Centrifugal Pump)

10/19/2010 12:24 AM

If it is the pump head being too low and valve throttling doesn't help, another solution is to put in a flow restriction orifce in the pipe so that you can move up the pump curve (to the left).

__________________
"Engineers simplify complex problems, and scientists vice versa."
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Motor Tripping Problem (Centrifugal Pump)

10/19/2010 4:06 AM

What is the shaft power requirement in kW when the pump pressure increase is multiplied by the volumetric flowrate though it?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Jun 2010
Posts: 75
#13

Re: Motor Tripping Problem (Centrifugal Pump)

10/19/2010 4:32 AM

Why have you installed 5 nos. of pumps for the said duty, I mean what was the selection criteria for selecting 5 pumps when only 2 run normally? What is the pump capacity-flow rate? Why have you reduced the impeller dia? Have done it in all the pumps?

BB Raina

Register to Reply
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: Aug 2007
Location: Australia
Posts: 1630
Good Answers: 20
#14

Re: Motor Tripping Problem (Centrifugal Pump)

10/19/2010 4:35 AM

Is this a new set-up or has it been in use some time.

If the system has been in use some time, what has been done if the pumps were running alright before this problem arose, e.g. pump maintenance, different valving, different diameter pipework, etc.

If it is a new set up, someone has stuffed up in pump/motor selection, incorrect dia. discharge piping (too small), etc.

__________________
TO BE. or NOT TO BE. That is the question!! The Bard
Register to Reply
Power-User

Join Date: Nov 2009
Posts: 296
Good Answers: 27
#15

Re: Motor Tripping Problem (Centrifugal Pump)

10/19/2010 8:58 AM

Others have made valid comments, just to add or repeat a few:

  • As it affects all motors the same way, forget the motors and look at the pumps and system.
  • Roughness of the casting of the impellers can have a major effect on the power consumed.
  • The reduction of impeller diameter should have reduced the power requirements.
  • You have apparently cast new spare impellers - the fact that they weigh more even though they are of smaller diameter could have a major effect, especially if the channels are wider.
  • If you have the curves for the pumps (original) then let us see them. If not, give the make and model and you can start looking at the generic family of curves to get some idea of what is going on.
  • At what differential head do the pumps trip and where is this point on the curve. (I assume you have no flow meter).
__________________
I have no special talent. I am only passionately curious. Albert E
Register to Reply
Anonymous Poster
#16

Re: Motor Tripping Problem (Centrifugal Pump)

10/19/2010 1:17 PM

Am I correct in assuming that your alignments have been checked thoroughly?

Register to Reply
Anonymous Poster
#17

Re: Motor Tripping Problem (Centrifugal Pump)

02/15/2011 1:26 PM

Dear Gurvir,

if I understood yr problem correctly, then before answering yr querry, may I first ask these questions.

1. When u r able to meet yr requirement with one or two pumps, why 5 pumps are installed ?

2. I presume further that u r running lesser flow thru colling tower that is why probably yr requirement of no of pumps have reduced

3. Did u collect data, as flow, disch pr, current, speed at full valve openning if VFD is not there?

4. On what reasons did the Impeller change ?

5. Adding some weight to impellers might not result in tripping, though it somewhat lead to little higher current but will surely not lead to tripping if pumps arenot very small in size.

6. Did you check the no load current, load current of al 5 pumps ?

7. pls check & inform the Shut off Pressures also alongwith all details regarding the pump flow, head, motor hp, speed etc. to enable me to understand and revert accordingly, probably I can help u in resolving this problem.

regds,

vivek srivastava

Register to Reply