Fire Protection for Transformers

03/15/2007 1:44 AM

What kind of Fire protection provided for Electrical transformers installed indoor and outdoors ?

__________________
NatNat7
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Feb 2007
Posts: 273
Good Answers: 3
#1

Re: Fire Protection for Transformers

03/16/2007 3:14 AM

NONE

Register to Reply
Member

Join Date: Mar 2007
Location: Europe
Posts: 5
#2

Re: Fire Protection for Transformers

03/16/2007 5:05 AM

Hi

Wet or dry type transformers ?

A sufficient controlsystem, that identify failures and disconnect the transformer in time to decrease the risk of fire.

Or is it fire-figthing solutions to transformers already on fire you are asking about ?

______________________

Without failures, no fire accidents !

Register to Reply
Associate

Join Date: Jan 2007
Location: Chennai, India
Posts: 28
#3
In reply to #2

Re: Fire Protection for Transformers

03/16/2007 5:25 AM

This is for protecting from possible externel fire for Wet type transformers at design stage.

Does it change drastically for dry type?

__________________
NatNat7
Register to Reply
Guru
Canada - Member - Our strength is our diversity

Join Date: Jan 2007
Location: Canada
Posts: 1024
Good Answers: 40
#4
In reply to #3

Re: Fire Protection for Transformers

03/16/2007 12:27 PM

Since transformers are built from metal, fire hazard is minimal. (the greator hazard would be an electrical short due to water ingress) so an overload protection is recommended.

They can produce heat. so proper ventolation and distance from flamables may be required.

The fire rating of whatever liquid is used as a dielectric should be checked. If it is highly flamable or reactive, you should either change the dielectric or engineer some protection such as insulation in the case, over-pressure release, protect or restrict materials around the transformer.

__________________
Perfection is a subjective and abstract concept.
Register to Reply
Power-User
Popular Science - Weaponology - New Member Popular Science - Cosmology - New Member

Join Date: Apr 2006
Posts: 261
#6
In reply to #3

Re: Fire Protection for Transformers

03/16/2007 1:38 PM

For Oil filled transformers, (Rarely installed indoors except in dedicated vaults):
All must be protected from weather or of proper type if outdoors.
If indoors most codes require a means of containing the coolant which may
escape if the transformer is damaged.

Fire rating / venting of the room is dependant on whether the coolant is of a
flammable type.
Because of the fire rated room, fire from external source is not considered a factor.

Consult local Codes.

Register to Reply
Anonymous Poster
#5

Re: Fire Protection for Transformers

03/16/2007 1:35 PM

I suggest to use a dry chemical powder automatic system with a rate of rise temperature detection.Or a carbone dioxyde system with the same detection.

Normand Audet /special hazard consultant

Register to Reply
Anonymous Poster
#7

Re: Fire Protection for Transformers

03/19/2007 10:10 AM

I can't quite get a handle on the question - maybe I shouldn't be answering it!

Are talking about power transmission transformers?

In the UK, our open air compound, oil filled, exposed insulator type connection transformers have no particular fire fighting protection.

Transformers which are in accessible indoor locations, with sealed chamber terminating boxes are protected by Emulsifier (sprinkler systems). Such locations would normally have large ventilation grills as part of the building and the sprinkler system would be of the Dry type (i.e. the sensor pipes and glass bulb detectors are filled with air pressure which holds the flap valve closed against the water pressure. If a bulb is burst, the air leaks out and the water valve flips open)

"All wet" systems would be liable to freezing when exposed to the cooling air coming from the outside. Oil filled transformers would be contained within a bunded area to stop oil escaping in the event of a leak or fire, allowing the sprinkler system to extinguish the burning oil.

Some of you are now going to say that you don't fight oil fires with water, but an emulsifier system produces a heavy wet mist blanket as opposed to direct jets of water.

Traditionally CO2 discharge was used in controlled access areas which was subsequently superseded by Halon, but this is also prohibited as it is a CFC gas.