LV Reactor Design and Construction

10/20/2010 4:59 AM

hi all

i need a simple guide for designing and construction of a three phase line reactor for starting of motor . which includes guides for

-selection of wire size

-selection of core size.

-determining of number turns for a specific motor size

it will be helpful if u can suggest me websites

thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: lv reactor design and construction

10/20/2010 6:09 AM

<...selection of wire size...>

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
2
Anonymous Poster
#2

Re: LV Reactor Design and Construction

10/21/2010 3:48 AM

Sizing a reactor:

The first rule is make sure you have a high enough amp rating. In terms of the impedance value, you will usually find that 3% to 5% is the norm with most falling closer to 3%. A 3% reactor is enough to provide line buffering and a 5% reactor would be a better choice for harmonic mitigation if no link choke is present. Output reactors, when used, are generally around 3%. This % rating is relative to the load or drive where the reactor impedance is a % of the drive impedance at full load.

Thus a 3% reactor will drop 3% of the applied voltage at full rated current. To calculate the actual inductance value we would use the following formula. L =XL/(2¶FL) Where L is inductance in Henrys, XL is inductive reactance or impedance in Ohms and F is the frequency. In general Frequency will be the line frequency for both input and output reactors.

Your drive distributor should be able to help you size a reactor for use with a drive. If you wish to calculate the value yourself, the following example may be helpful. If a 3% reactor was required for a 100 amp 480 volt drive, a 100 amp or larger current rating would be required. The drive impedance would be: Z=V/I or 480/100 = 4.8 ohms. 3% X 4.8 ohms = 0.114 ohms inserting this 0.114 impedance in the equation for inductance we get a value of about 300 Microhenrys.

Register to Reply Good Answer (Score 2)
Anonymous Poster
#3

Re: LV Reactor Design and Construction

10/21/2010 5:57 AM

Impedance rating and Selection of the Line Reactor: (3% or 5%)

Definition:

Z %= (VD X 100) X √ 3 / VS

Z = Impedance

VD = Voltage drop across reactor at rated current to flow through it

VS = Voltage supply



Usually by choosing 3 % impedance line reactors can meet need for the most solid state applications in North America. Where there are high line disturbances in the involved circuits, a 5 % impedance reactor may be required. Normally these units are used in the particular occasion where there are strict limitation concerning harmonic distortion and noise level.

Register to Reply
Anonymous Poster
#4

Re: LV Reactor Design and Construction

01/03/2011 6:44 AM

hi

my name is v.naghashi

I am MSC student in iran

and now I am working on your topic with research form.

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

Previous in Forum: How To Change The Display Mode of UniDrive 3405   Next in Forum: Fanuc R-J2

Advertisement