Fault Current

10/20/2010 10:17 AM

How do determine the fault current value of 11KV/ 415 V, 630 KVA transformer system?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: fault current

10/20/2010 10:26 AM

Divide 630kVA by the voltages to obtain amperes. Anything above each of those two numbers would indicate an overload fault.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#2

Re: fault current

10/20/2010 10:40 AM

On the 11kV side, available fault current depends on the system upstream, either the utility's source or the larger transformer that feeds this one, plus the effects of lengths of cable and bus and any contribution from generation or motors on-site. It is not trivial to analyze.

On the 415V, it can be approximated by calculating the Full-Load Amps of the transformer kVA / (kV * sqrt 3) = 630 / (0.415 * 1.732) = 876 amps. Divide this by the transformer's percent impedance expressed as a decimal (e.g., 5.5%Z = 0.055) to get a rough estimate of max fault current at the transformer secondary. Assuming this unit is about 5.5%Z, available secondary fault current is about 16kA. To this would also be added contribution due to motors on the circuit, which feed back into the fault while they are still spinning as generators.

Again, not a trivial analysis. If you want to calculate it all out by hand, it is possible - the procedure is documented in any textbook on power system analysis, or the IEEE Brown Book (IEEE Recommended Practice for Industrial and Commercial Power Systems Analysis). Easier way is to get software such as the SKM Power*Tools Analysis, but that entails cost and a training/learning curve.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer