Power Cable Installation (4 Core With Shield?)

10/21/2010 6:50 AM

We are using FONDINSONSO AP-5125 Plug and EPC1-1P125B Socket. It is a 5 pin socket and plug rated at 125A. The cable that we use is CU/XLPE/PVC/SWA/PVC-FR 0.6k/1kV. It is a 4 core cable with a shield. The length of the cable is 100m. 3 cores are used as live and 1 as neutral. The cable shield is grounded to earth at both ends. Is this type of installation correct? Or do we need to use a 5 core cable and use the fifth core as grounding instead of the cable shield? This installation is used to supply power to a remote distribution panel from a generator set.

I have asked this question to a local company which does power cable installation and the answer was given as below. I search around the net and found some articles saying that the shield is supposed to be grounded. Which is correct?

"Basically there should be 4 numbers ( 3 phase), Red, Yellow , Blue, Neutral . The earth comes from the grounding of the generator set that is connected to the earth pit., therefore altogether, there should be 5 numbers of cables, that is connected from the generator to a switchboard panel and since the distance is 100 meters, then you probably use 4 numbers of cables / 4 core connected to the switchboard, the earth cable will be probably from the switchboard earthing pit. If that is so, please make sure the earth resistance measurement be less then 1 ohm.

FYI cable shield (armoured) is never used for earthing purpose. They are used as a mechanical protection for the internal cables/ core. To answer your question below, please check if there is any earthing done for the generator and the switchboard first, and then you will be safe. Continuity test on the shield is not necessary and would not pose any issue."

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2010
Posts: 348
Good Answers: 10
#1

Re: Power cable installation (4 core with shield?)

10/21/2010 7:31 AM

It is true that the armor wire is not used as an earth continuity conductor although it will serve as an equipotential bond between separate earth systems at the two ends.

You can avoid additional earth wire from the load end if you can arrange earth pits there as well.

Reason for not using armor as an ECC is that it can overheat in case of serious faults thus causing damage to cable insulation.

Requirement of less than 1 ohm relates to local codes of your area.

__________________
Knowledge sharing is a WIN-WIN situation
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Power Cable Installation (4 Core With Shield?)

10/21/2010 10:24 AM

Follow local wiring codes applicable in that location. In the UK, for example, it would be British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Dec 2007
Location: Brasov, Romania
Posts: 255
Good Answers: 7
#3

Re: Power Cable Installation (4 Core With Shield?)

10/22/2010 1:51 AM

As far as I know shield is not the same as armour. The shield is made up of electrical conductor for grounding purposes to evenly distribute the electrical field along the insulation, the armour mechanically protects the insulation.

__________________
The time is ......now
Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

mountk2 (1); nikolay (1); PWSlack (1)

Previous in Forum: Solution for Busduct Noise?   Next in Forum: Ideal LA Rating
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement