Generator Load

10/22/2010 10:15 AM

What is the disadvantages and risks (if any) if the diesel generator is running at low load less than 20% of its full laod capacity)

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#1

Re: Generator Load

10/22/2010 11:24 AM

Unless specifically stated in the equipment documents, I see no risks or disadvantages to running below 20% FLC.

Your fuel demand/use will be lower in terms of if your were running 80% - 100% FLC instead.

__________________
The first 5 days after a weekend are always the hardest................................
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Generator Load

10/22/2010 1:05 PM

Prolonged operation of this engine at only 20% of its design capacity will expose it to an all most certain case of "Wet Stacking".

Wet stacking is what happens when an underloaded diesel (or gas engine - though much more of an issue with diesels) is ran for extended periods of time at the reduced power levels. Basically... diesel fuel will not be "burned" or consumed properly and ends up accumulating in the exhaust train and will, over time, concentrate in the engine's lubrication system.

Many a diesel has been taken out by journal failure because of poor lubrication due to wet stacking.

Here is a link for more reading...

http://www.logcom.usmc.mil/smc/secrepmaint/files/maintenance%20trends/April%202007%20Wet%20Stacking.doc

You might want to think about adding a load bank to keep the engine power up over at least 60% of design.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Generator Load

10/22/2010 2:16 PM

Well, GA from a non generator expert. Who says old dogs can't learn.

I would have agreed with KJK/USA. Shows what I know.

And, KJK/USA I like your new avatar.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4
In reply to #2

Re: Generator Load

10/22/2010 7:30 PM

Excellent and concise link.

In addition, if the exhaust temperature falls below the exhaust gas dewpoint, sulfuric acid in the gas can condense and cause corrosion in the exhaust system. That would be less of a problem with low-sulfur fuels.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Commentator

Join Date: Oct 2010
Location: Quantum Dimension
Posts: 85
Good Answers: 1
#5

Re: Generator Load

10/24/2010 10:47 AM

When you have an generator running for longer periods on a very low load

the valves of the diesel will carbonise as well as the exhaust manifold

Then when you need the generator then at full capacity she will not bring no more

then those 20 - 40 % and you have to decarbonise it for hours first.

We call this reglowing the exhaust

This happens unfortunately a lot even for units in the army and hospitals !!

they 'think' let the e-sets running for a few hours and then everything is ok.

Nothing is further from the truth

L8rz.. T L.

__________________
Humans use 10% of their mind , WE take the rest
Reply
Reply to Forum Thread 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

KJK/USA (1); lyn (1); North of 60 (1); timelord (1); Tornado (1)

Previous in Forum: Inrush Current   Next in Forum: Control Circuit

Advertisement