Voltage Drop Due To Heavy Load

10/23/2010 1:10 AM

Hi, I have a 3phase 250kW compressor to be fed from a distance of 180 Mtrs. Starting current of the compressor goes to about 10times the running current, which is about 480A. Normal voltage drop calculation will not be applicable for such high starting current I presume.. In this situation, how can I decide the cable size? Normal Voltage drop calculation for this length (180Mtrs) and 480A load gives me the cable size as 2 Runs of 4cx185 sqmm Copper cables. Going for the next size will be enough?

Register to Reply
Pathfinder Tags: voltage drop
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Mar 2010
Posts: 105
#1

Re: Voltage Drop Due To Heavy Load

10/23/2010 6:28 AM

Dear Sir,

Please give some more details (1) Comp.Motor Voltage as in the name

plate (2) The frequency of Start / Stop say per hour (3) Will the Comp be

running fully loaded or % of loading (4) What is the present method of starting ?

(5) What do you mean by "which is about 480 A"- Starting Current Or running

current ? (6) Is it a HT motor , because 48 A @ 3300 V will give 274 Kws.

which is nearest to 250 Kws taking the current as given by you.

Please think about soft starting.

Manroop.Chennai.

Register to Reply
Anonymous Poster
#2
In reply to #1

Re: Voltage Drop Due To Heavy Load

10/23/2010 7:40 AM

Manroop,

1/ read question first

2/ if there's insufficient information, say so

3/ don't make assumptions

4/ think before answering

Register to Reply
Power-User

Join Date: Mar 2010
Posts: 105
#15
In reply to #2

Re: Voltage Drop Due To Heavy Load

10/26/2010 8:23 AM

Dear Guest,

Thanks for your advice.Also do not hide as Guest !. Any how I am glad to note the original question is a bit ambigous as noticed by Mr.JReaf . Furthur it shows you did not read the words fully and advice others & please avoid this sort of comments in future. Atleast I was able to assume something which you did not try at all. Incidentally Mr. JReaf has the highest ratio 11.25 % ( Good answers / posts).

Excuse me if I am a bit out-spoken on this and it is a good intention to have some decorum in CR4.

Manroop.Chennai

Register to Reply
Member

Join Date: Oct 2010
Posts: 5
#3
In reply to #1

Re: Voltage Drop Due To Heavy Load

10/23/2010 8:19 AM

1) Motor Voltage is 400V.

2) Frequency of operation shall be once in 4 to 5 hours, with a running time of about 1 hour.

3) Compressor is expected to run at about 85% load, but for calculation purposes, let us consider it runs on Full load.

4) Star/Delta starting, it comes with its own panel with star delta starter. We have to lay cable from Substation to this panel.

5) About FLA, I assumed it to be 0.85 x 250kw, at 400V 3phase power.

Thank, Dilip.

Register to Reply
Anonymous Poster
#4

Re: Voltage Drop Due To Heavy Load

10/23/2010 9:50 AM

For this size compressor you need to get a good starter and also unload the compressor by closing induction valve. Is it delta/Y????... The resistance of stator wiring is probably comparable to the resistance of power line so the voltage drop could be up to 240 V.

Is this a new project or you deal with existing compressor? If the installation exists then you just measure voltage drop if it is new, you better think to get a good frequency conversion with automatic start up. Going to the next size would be waste of energy that costs much more! Do it right.

Is the motor of the compressor a three phase squirrel cage or wound rotor?

You could also use old style that employs ... got yourself a book Handbook of Electrical Engineer" that would provide you with reaqdy to go systems.

Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5

Re: Voltage Drop Due To Heavy Load

10/23/2010 9:58 AM

I would suggest you to see this thread first: http://cr4.globalspec.com/thread/57342/Cable-Selection-as-per-Theory-Calculation. It has much detail about the cable selection.

I understood that it doesn't have the information about the permissible voltage drop during motor starting. You need to calculate the voltage drop during motor starting and select the cable so that the motor terminal voltage doesn't drop below 80% of the motor rated voltage (it is better to verify it with the motor manufacturer). If you select the cable so that the voltage drop at running condition is below 2%, it will satisfy the starting condition voltage drop (because the starting current is 10 times of running current).

If the compressor load is supplied by local generator, you also need to make sure that the generator capacity is well enough for the motor starting (see http://cr4.globalspec.com/thread/58246/Power-Generator-Sizing)

Hope it helps.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Voltage Drop Due To Heavy Load

10/23/2010 10:02 AM

Dilip, you may find this cable calculator useful http://www.aeicables.co.uk/csdisclaim.asp it is to BS7671, I don't know what reg's you work to.

With the compressor being star/delta starting the loading won't be as bad as you think. Also it's not usual to rate the cable for starting load but for running load.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: Voltage Drop Due To Heavy Load

10/23/2010 3:29 PM

"Starting current of the compressor goes to about 10times the running current, which is about 480A."

Is this something you have measured or is this theoretical on your part? If it is measured, what kind of motor do you have here? Starting current should not be more than 6 times (600%) of motor nameplate Full Load Current when started DOL! So assuming the FLC was 480A (the way you word things is a little ambiguous), your starting current should not have been more than 2880A.

Or maybe you are confusing "Inrush Current" which is a very very brief spike of current that occurs when the motor windings are magnetizing, with "Starting Current" which is the peak current after the inrush that the motor will pull during acceleration. If you made this mistake, you do not need to consider the "Inrush" current in your voltage drop calculations and cable selection.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8
In reply to #7

Re: Voltage Drop Due To Heavy Load

10/23/2010 5:40 PM

I would just pick you up on one point. 6 x FLC was for older motors as I found out by bitter experience.
Strange as it may seem it was a 250KW compressor, the motor had burnt out. So following company policy the old motor was scrapped and a new high efficiency motor was ordered.
Came the day for it's first test run. Radio the control room to tell them to start the compressor. Clunk, the contactor closed, bang, the MCCB opened and Tony's sh^ting himself wondering how he could get 3 wires messed up.
Modern high efficiency motors can be up to 9 x FLC. The new MCCB I had to fit was 7000A as against the original 4000A inrush withstand. Thermal characteristics were the same.

Fitting the new MCCB is a different story, "it's the same footprint so a direct replacement", NOT! 2 hours to fit turned in to 10!

Dilip, the cable for the compressor I altered was 150mm with DOL starting.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Oct 2010
Posts: 5
#9
In reply to #8

Re: Voltage Drop Due To Heavy Load

10/24/2010 4:01 AM

Hi,

Thanks to all of you who took interest to answer my query... Its great to find that there are people out there to help. Now, I find that the cable need not be sized as per starting current, but as per the running current only.. Anyway, to be safe, I am now going for next size, ie, 2 Nos x 4Cx240 sqmm Copper cable, which solves the problem..

It has been a great experience...

Regards, Dilip.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#10

Re: Voltage Drop Due To Heavy Load

10/24/2010 2:19 PM

Dilip, that is twice the size needed. Added to which you only need 3 core.
It's a waste of money!

Did you look at the cable calculator?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Oct 2010
Posts: 5
#13
In reply to #10

Re: Voltage Drop Due To Heavy Load

10/25/2010 1:42 AM

Hi, Thanks.. This is a job which I am negotiaing the price with the client - the original offer I sent them with 2 nos 4x185 sqmm cable shall be now revised with 4x240 sqmm.. There is a common Power/control panel in built for the compressor, which needs neutral, hence 4core cable...

Regards, Dilip.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#14
In reply to #13

Re: Voltage Drop Due To Heavy Load

10/25/2010 6:44 AM

If you're only wanting the neutral for control use a 3 & ½ core

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Member

Join Date: Oct 2010
Posts: 5
#16
In reply to #14

Re: Voltage Drop Due To Heavy Load

10/27/2010 8:26 AM

Hi , You are right, But here in Dubai they use either 3 or 4 cores... its a waste of money, which is not realized by Gulf countries.... In all GCC, its the situation...

Regards, Dilip.

Register to Reply
Power-User

Join Date: Jul 2007
Location: The cigarette-stained drunkard living in the cardboard box outside Marks & Sparks delivery entrance, Eastgate Shopping Centre, Basildon.
Posts: 487
#11

Re: Voltage Drop Due To Heavy Load

10/24/2010 3:04 PM

Geez, if I was doing it, I'd use British Standard 7671. You know, this is about the most frequently asked question in CR4, Mate, and the fact that you 'aven't done yer research and 'aven't the foggiest how to tackle the problem other than ask some other nana to do it over the interweb does rather worry me. I mean, WTF are they paying you for? <Wheeze>

Don't these people know how to do this stuff for themselves any more? <Splutter, cough>

__________________
Essex jobs for Essex yobs! <Burp>.
Register to Reply
Associate

Join Date: Jun 2010
Location: INDIA
Posts: 27
Good Answers: 1
#12

Re: Voltage Drop Due To Heavy Load

10/24/2010 11:32 PM

GET THE MOTOR AND CABLE DATA SHEET.

1.STARTING CURRENT .

2.STARTING PF -Φ

3.CABLE -R& Xlmtr

Calculate the voltage drop by √3 I(Start)(RcosΦ+Xsin Φ).

Refer the system design criteria whether this voltage drop is within designed limit or not.

__________________
S BHATTACHARYA
Register to Reply Score 1 for Good Answer
Anonymous Poster
#17

Re: Voltage Drop Due To Heavy Load

11/01/2010 5:34 AM

Hi not sure what kind of starter you are using, for starting the compressor, but i would presume that the starter is DOL, if it is going to draw that much current, I would size the cable as to the motor rated load as this would give you a bit of a soft start.

But 10 x motor rated current? I do find this very high, how did you come up with this current calculation?

I have found on previous projects DOL is only about 6 x full motor current, older soft starters draw 3 x full load current and star delta starters to be about 2 x full load current if set correctly.

Cheers

Joe

Register to Reply
Register to Reply 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); bsekhar (1); JRaef (1); manroop (2); msamad (1); pishdili (4); Stinky Pete (1); TonyS (4)

Previous in Forum: Electrical Engineer   Next in Forum: Resistors in Parallel

Advertisement