Linking Fire Alarms

10/23/2010 3:39 PM

Dear members, I would like someone to advise me on how I can link 2 buildings which have different fire alarm systems so that when there is a fire in one building the people in the other building can hear the alarm. One building is installed with a menvil system wheras the second one is evasafe. I was thinking of 2 options:

1. To install a sounder from each of the building to other.

2. To install a radioLink Smoke alarm in either of the buildings.

Grateful for your advises

Luyombya

__________________
"It doesn`t make sense to hire smart people and then tell them what to do, hire smart people so they can tell you what to do."--- Steve jobs.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#1

Re: Linking fire alarms

10/23/2010 4:02 PM

Add a relay to the alarm output in bldg A and run a normally closed contact pair from the relay to a zone on the alarm in bldg B. Repeat the other way around.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Linking fire alarms

10/23/2010 5:12 PM

Sounds simple enough to me, but it's Saturday night and the highland waters are taking effect.

Logical really just break in to a loop of the opposite system.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Oct 2010
Location: Philippines
Posts: 38
#3

Re: Linking fire alarms

10/24/2010 6:35 AM

Wire bldg B's siren or output terminal (or PGx / PGy) into a zone of bldg A Make sure zone used is set to NO

OR

Depending on distance, hook up a second siren and run the cables to the next building.

Register to Reply
Active Contributor
Safety - Hazmat - New Member Technical Fields - Project Managers & Project Engineers - New Member

Join Date: Dec 2009
Location: Kampala
Posts: 24
#4
In reply to #3

Re: Linking fire alarms

10/25/2010 3:28 AM

Thanks all for your input but back to Ton`s 2nd option. The distance between the bldings is not all that great approximately 30m from one siren to where I can install a second siren. Does this mean that I just have to loop the 2 sirens together? likewise do the same for the other set of siren from the other blding?

__________________
"It doesn`t make sense to hire smart people and then tell them what to do, hire smart people so they can tell you what to do."--- Steve jobs.
Register to Reply
Member

Join Date: Jul 2010
Posts: 8
#5
In reply to #4

Re: Linking fire alarms

10/25/2010 6:55 AM

Yeah sure. Simply connect the sirenes in parallel. Just b sure you use sirene compatible with the system.

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#6
In reply to #4

Re: Linking fire alarms

10/25/2010 8:35 AM

Dont do this. Fire alarms are not so "cut and dried" that you can just "add" things to them. Adding the sirens in parallel as suggested would, almost guaranteed, void the certification from the manufacturer. If something were to happen, your potential liability is large.

If you do proceed as suggested, bring in the manufacturer to re-certify the installs on both units. Go the input to a zone route.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7
In reply to #6

Re: Linking fire alarms

10/25/2010 8:59 AM

I may have mis-read the intent. If you intend to keep the two alarm circuits separate, adding alarms in parallel is ok as long as the maximum drive current for the ouput is not met.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Apr 2009
Location: USA, Florida
Posts: 1595
Good Answers: 125
#8

Re: Linking Fire Alarms

10/25/2010 11:45 AM

Do not tie the panels together using cross alarm contacts (each panel alarm contacts activate other panel input alarm zone). If this is done an alarm reset can only occur with someone standing at both panels. Adding alarm devices to either panel will require new power supply and standby battery calculations. Your desire to sound alarm in both buildings is not a code requirement, therefore you can treat each non-alarm building as an non-required annunciator. Install an interval delay relay in each panel and set the delay time to 1 second. The power to energize the relay comes from the other panel, switched through alarm contacts. The N/O contacts from the relay ties to an input circuit in the panel. You can even double lug an existing (used) input circuit as long as you don't add an end of line resistor to the relay. When Panel A goes into alarm it energizes the interval delay relay inside the other panel, placing that panel into fire alarm as well. After 1 second the relay contacts return to normal state, even though still energized. Now each panel can be reset independently.

__________________
An obstacle is something you see when you take your eyes off the goal.
Register to Reply
Associate

Join Date: Oct 2010
Location: Philippines
Posts: 38
#9

Re: Linking Fire Alarms

10/25/2010 8:36 PM

Your better off treating them separately... No worries of voiding any warranties, no code violations, no complications, no headaches.

If you treat it as a "remote" or second sounder / annunciator you will not have to worry about each panels idiosyncrasies (and may even have a spare output on the TB to use). If there are wireless options then even better provided you have line of sight. 30 meters should not be a problem for 24 VDC.

I am assuming your gonna place the 2nd unit at the command center of bldg A (manned station)? You may wanna consider using a strobe so as not to panic people unnecessarily cause if wired into a zone then when one trips, all will trip. This may cause confusion/problems.

Cheers bro

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

luyombya (1); North of 60 (3); TonCab (2); TonyS (1); uchesteve (1); WJMFIRE (1)

Previous in Forum: Temporary Earthing/Grounding   Next in Forum: Brows

Advertisement