Anonymous Poster

Temporary Earthing/Grounding

10/23/2010 11:06 AM

Hello sir/madem, I am working in DUBAI ELECTRICITY AND WATER AUTHORITY. My job is to handle 11 kv sub stations maintenance which are isolated from both far ends(RMU system).Now there is a chance of potential hazard from low voltage distribution which goes to consumers.(If they use gen set without disconnecting regular supply rout).We are asking to tie around bare conductors across main earthing and out going cables.But I am asking them to provide standard insulated local earthing kits. Pls suggest.

I have registered for cr4 just now. confirmation yet to get

my email id is ahmed.iqbalmys@gmail.com

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
2
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Temporary Earthing/Grounding

10/23/2010 3:08 PM

From the RMU the feed goes to a transformer and then a distribution pillar?
I would suggest you remove all fuses from the pillar. Unfortunately manual earthing of the out going feeders is required, I've not come across any with dedicated earthing arrangements.
This is a common problem worldwide, there have been several linesmen killed in the UK due to farmers starting up gen sets and back feeding in to the system.

PS don't include you email address in posts.

__________________
The reports of my death are greatly exaggerated.
Reply Good Answer (Score 2)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: Temporary Earthing/Grounding

10/23/2010 3:45 PM

Do you have a set of air breaks at the incoming feed to your 11kV sub-station? If so, open the breaks and ensure that the breaks are locked open with multiple lock out tag out devices. Visually ensure that all 3 phase breaks are in fact open.

If you do have air breaks, once you get them open, you will need to bond all 3 incoming local phase conductors (after the air breaks) to each other, and to the neutral (if present), then bond it all to a local ground.

If you do not have air breaks and must depend upon an upstream device that is not under your control, open it, lock it out and install the bonding jumpers to ground at the upstream device then install more bonding and grounding jumpers at the local termination point on your HV stack. This requires a second set of jumpers but ensures no moron upstream can energize the section you are working on. I would go so far as to drop the incoming phase conductors from the stack.

Do not just make up your own sets of bonding and grounding jumpers. Jury rigged clamps have been known to "jump" off a line when energized in error due to the magnetic field produced under fault conditions.

Many firms sell utility grade "clamps" and bonding and grounding jumpers especially made for this purpose. Use them!

Here is a link for you...

http://shop.hilineco.com/index.php/cPath/546_427

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: Temporary Earthing/Grounding

10/23/2010 4:34 PM

Re-read the question, it's the LV side that is the problem, HV earthing is handled by adjacent RMU's.

Back feeds on LV systems is a constant worry.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#4
In reply to #3

Re: Temporary Earthing/Grounding

10/23/2010 8:03 PM

Agreed... he just needs to open his outgoing over current devices. Those he should have full control of.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply