Anonymous Poster

Need Help in IR Value and Test Lamp Test of Submersible Pump

10/26/2010 7:29 AM

We have submersible pump of 85HP,440V with Auto Transformer Starter.

Before one month Pump took very high current 320Amp on each phase after that we had checked each winding with test lamp with reference to ground and Bulb glows..

We had pulled out the Pump and revinded it. After that We rechecked IR value of Winding and it found ok. After that we pull down The Pump on Borewell.

When we start the motor-pump it took 110 Amp on each phse And motor runs healthy up to next one day only.

After that It's again take very high current 320Amp on each phase.

Now we have checked IR value of each motor terminal with Earth and it show "0" value but the same Time when we are doing Test lamp test between each motor termonal with respect to earth but Bulb doesn't Glow.

What we conclude from above measurement. It's winding again burn out

Reply
User-tagged by 1 user
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Active Contributor

Join Date: Oct 2010
Location: Libya(Bangladeshi)
Posts: 15
#1

Re: Need Help in IR Value and Test Lamp Test of Submersible Pump

10/26/2010 8:20 AM

if you have volt meter you should measure voltage from line to line.anotherway you can measure voltage you will connect in series 2 lamps(220VOLTs) ,then two terminal of lamp put with R ,Y & Y,B & B,R terminal of system voltage,if light lit up with same intensity then ok. if one phase is short with another phase then what will happen?

IF you test 1 lamp with every phase to ground then light will glow with same intensity

,so far my idea ,your motor was working like R=Y(short) and B ,so everytime you have got lamp test result from phase to ground.

I have just shared my idea.In practical case ,normally it happen.

__________________
asadmawa
Reply
Power-User
Canada - Member - New Member

Join Date: Feb 2010
Location: The Great White North
Posts: 185
Good Answers: 13
#2

Re: Need Help in IR Value and Test Lamp Test of Submersible Pump

10/26/2010 12:41 PM

It is possible that your pump is mechanically locking up due to a seized bearing or obstruction and what you are seeing is locked rotor current. If your overloads were set too high or weren't fast enough the motor may have burnt out before the overloads tripped. You may have been luckier the second time.

Also check for moisture ingress.

__________________
Knowledge makes what was impossible, seem easy.
Reply
Member

Join Date: Sep 2010
Location: Gandhinagar,India
Posts: 9
#3

Re: Need Help in IR Value and Test Lamp Test of Submersible Pump

10/26/2010 1:12 PM

We have Bimetalic type O/L Relay and set it on min (115 Amp). so at instant heavy current it doesn't trip.

My confusion is when we check IR value of each terminal of motor against the ground it show 0 value (means S.C any wdg with Ground) but when we check it by use of single 60w bulb (230v) and give phase to bulb to any terminal of motor to earth. Bulb doesn't glow (It should be glow in the case of S.C).means winding show O.K in Test Lamp Method ??

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4

Re: Need Help in IR Value and Test Lamp Test of Submersible Pump

10/26/2010 11:46 PM

Refer manufacturer's cataloque for cooling of motor by distilled water or transformer oil. Also embed a thermistor in motor winding to give an alarm and trip the motor if temp of wdg exceeds the limit

__________________
pnaban
Reply
Anonymous Poster
#5

Re: Need Help in IR Value and Test Lamp Test of Submersible Pump

10/27/2010 1:48 AM

I hope that when the IR is 0, it means that your winding is shorted with the body and taking earth as ground. The Bulb will not light as the current is flowing to the earth and not through the resistance of your bulb. If your winding not get black and still in condition then Please use high temperature liquid varnish to brush over your windings and let it dry .Check your IR values before loading the Motor. Good luck

baywatch

baywatchu@yahoo.com

Reply
Anonymous Poster
#6

Re: Need Help in IR Value and Test Lamp Test of Submersible Pump

10/27/2010 4:48 AM

Please explain to me how this test with the bulb was conducted?

Why did you not just do an insulation resistance test on the motor windings to earth in the first place?

This test that you did with the test lamp, of which I am not familiar with, what was the wattage of the lamp used in the test?

Have a look at the windings from the burnt out motor, they should show some signs of maybe a slow overheating or some other failure.

What kind of water are you pumping, is this bore well dependant on tidal movements, don't forget that most sub-mervisable pumps require water cooling, was it always covered in water?

Cheers

Joe

Reply
Anonymous Poster
#7

Re: Need Help in IR Value and Test Lamp Test of Submersible Pump

10/28/2010 1:02 AM

Problem is sortout We have pulled out submersible pump again.Decoupled the motor-Pump. Motor runs on no load and take 40 amp at noload..but pump's shaft did not moved. When we dismentaled each stage og pump, we found some sand inside the pump's stage no 4 which cogged the pump and motor took very high current.

We also measure meeger value for each terminal of motor with earth (including Flate cable) and It show o value but when we cut the Flat Cable from motor's cable and again measure the IR value of Motor terminal with Earth ( without Flate cable) . It show 12megh ohm !!. We also measure IR value of only Flate cable (without motor) and it show 10 megha ohm !!!!!!!!!!.

Reply