hii all As cable size goes on its current carrying capacity decreases comparatively why so??? example: 3.5cx25sqmm AL cable can withstand= 65amps(aprox), 3.5cx35sqmm AL cable can withstand= 80amps(aprox), 3.5cx50sqmm AL cable can withstand= 110amps(aprox), 3.5cx70sqmm AL cable can withstand= 140amps(aprox), 3.5cx95sqmm AL cable can withstand= 160amps(aprox), for 25sqmm current carrying capacity is almost morethan double...nearly 65amps where as for 95sqmm current carrying capacity is lessthan double..nearly 160amps WHAT IS THE REASON............
Re: Cable rating?????????????
10/26/2010 10:16 AM
Please read up about the skin effect (click here).
10/26/2010 10:20 AM
you are talking about derating factor because if current is more then inductance of line will increase as well as the effect of capacitance,thats why larger cable size taking less than your expectation as compared to low flow(A) current cable.
Just I will give you one important things that if cable size less than or equal to 16 sq.mm
then Z=R,i mean capacitance and inductance consider to be nearly zero,
If cable size 3or 4x 25sq.mm or larger then z=root(R square + X square)
so not only current rating of cable but also to consider voltage drop we have to design cable size.
asadmawa
10/26/2010 10:24 AM
Sigh
I guess that you do not know anything about the fundamental laws of electricity. From your question I can tell you know nothing about Ohm's law, the conductivity of metals and insulators, or even how to calculate the power released in a fixed resistance with a known current.
Ok, here's a layman's explanation.
The current limits you've found are the continuous current limits that these wires can handle at room temperature. At this current the power released per meter of wire by the resistance per meter of this wire will not cause the insulation around this wire to fail. Different cable constructions can handle higher amount of current before reaching an insulation failure condition.
Re: Cable Rating?
10/26/2010 11:31 AM
Even before taking account of skin effect, the ampacity of a cable would relate to the cross-sectional area; i.e., proportional to d2. However, the heat generated must be dissipated through the wire surface and the insulation, whose area is proportional to d.