Anonymous Poster

AC Generator AVR

10/29/2010 3:30 PM

hi all,

on some ac generator automatic voltage regulators, the manufacturer says that the resistance of exciter field stater should not be less than 10 ohms.

why is that?

i have three phase generator 380v, the resistance of the exciter stater coil is 4 ohms, the maximum voltage is 17 vdc, the amps is 4.25 amps. this was on the name plate.

i have new voltage regulater, continuous current is 6 amps, but on its specifications says that the field coil resistance should not be less than 10 ohms.

i tried the voltage regulator on this generator and it worked fine, the voltage output from the regulator to the field was 5vdc, 1.25 amps when the generator without load.

now lets say the generator will be full loaded, on the name plate says the exciter amps will be 4.25 and the regulator can carry 6 amps, so what is the problem on that.

as i can see now, this regulator is working fine on a generator with field coil resistance less than 10 ohms!

so what is the reason of saying this by the manufacturer?

many thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: ac generator AVR

10/29/2010 4:25 PM

If it works fine then no need to ask questions,be happy with what you have.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: AC Generator AVR

10/29/2010 6:57 PM

Well there are a whole lot of things that it could be that explains why the manufacturer wants the exciter field windings to have no less than 10 Ω resistance. They all hinge on the fact that some part of the system will no longer will act linearly if the resistance is less. I suspect that the magnetics can saturate if the resistance is less than 10Ω. But a few of the other possibilities could be an over heating problem of the windings, the exciter control circuitry might be damaged, the carbon brush contacts will self heat to the point of ignition, the engineers wished to annoy people by not explaining generator design to the customer.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
2
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#3

Re: AC Generator AVR

10/30/2010 1:12 AM

10 ohms 6A makes up to 60 for which it is perhaps designed to work. However due to 4 Ohms in the load, its output voltage drops to 5V giving limited current of 1.2A and rest of the power sure is wasted somewhere inside for the loss of 55V X 1.25A which is a very big loss and a lot of heat may get generated and soon something may fail or blow inside the driver.

Instructions are serious one so never underestimate them. If you are happy for it to look like working for a while and becoming dead forever soon then go ahead.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Reply Good Answer (Score 2)
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#4
In reply to #3

Re: AC Generator AVR

10/30/2010 6:04 AM

GA from me.

The AVR output circuitry must have an internal resistance of ~10Ω therefore, if the external resistance (here the exciter stator) is less than that it will make the AVR to dissipate more power internally that it is giving out. In this case, 1.25A^2 x 4Ω = 6.25 W given out while dissipating internally 1.25A^2 x 10Ω = 15.63W. For a full 4A, 16x10 = 160W inside against 64W in the exciter.

Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#5
In reply to #4

Re: AC Generator AVR

10/30/2010 10:26 AM

Not correct.

You are assuming that inside resistance is 10 ohms.

Inside voltage should be 60V or more when you have open circuit for it is deliver 6A into 10 ohms load. Power 60VX60V/10 Ohms = 360W.

Something is going wrong inside as it delivers only 1.2AX1.2AX4 Ohms= 5.76W

What is happening to the power driving capability of the device?

If it is a current source then 6A must be delivered and if it is a voltage source then 60V must appear.

Perhaps it tried to deliver 60V and then power becomes 60VX60V/4 Ohms = 900W.

Perhaps its overcurrent sensing device trips and you get some minimum 1.2A still from a nearlt dead system.

Using device improperly is not engineering and it is called :JUGAD" in India, which means somehow using things to get some results for some time. Things appear working for a while and sometime better than Original.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6
In reply to #5

Re: AC Generator AVR

10/31/2010 8:43 AM

"Not correct" ??

First of all, please think about it before making such a statement:

1- AVR = automatic Voltage regulator: It regulates the Output Voltage of the main alternator by CONTROLLING (Varying) THE Current in the Field Coils. The current is here the subject. Therefore, The AVR is a Current Source: The Output Voltage of the AVR is Varied in such a way to Increase or reduce the current into the exciter field which has a fixed resistance of 4 Ω here.

2- Therefore, the Voltage output of the AVR is not fixed to 60 V DC. It Cannot be otherwise how do you regulate ...??

3- The Exciter Output Voltage will Vary and produces a varying current into the main field. Which brings you back to the fact that the AVR is basically a current source.

4- Now: Since the exciter in this discussion has a resistance = 4 Ω , and the nameplate says that the full load exciter field current = 4.25 A, the required voltage from the AVR will be 17VDC (4.25 A x 4 Ω), and the nameplate reflect this(!).

The New AVR is rated at being able to supply (SINK) 6 A and needs to be connected to a minimum resistance of 10 Ω. There is no mention of the output voltage from this AVR. This is because you can calculate it to be : 6 A x 10 Ω = 60 VDC . But this does not meen that the voltage is fixed!! It can even be higher if the AVR is driven to sink more than 6A into the 10 Ohms it is rated for.

The Problem is this: The AVR Output stage has an internal resistance as seen from the outside. This resistance determines the internal losses that will be dissipated when operating. The 10 Ω value means that if the Load resistance is less, the internal losses will become higher than the power supplied to the load at whatever level, from no load situation (minimum excitation current) to the full load situation (max excitation current). This ia the main reason why this value is given by the manufacturer. Usually, this is the point where the internal loss = the external load power used. { It could be less if the manufacturer chose to so that the ratio could be less internal loss for a load: 50/50, or 40/60...}

Therefore, Hooking the AVR to a 4 ohm exciter stator will make it work less efficiently since it will spend more energy internally than it is delivering to the load. If at full load, when the exciter field will be taking 4.25A, the power delivered is (4.25)² x 4 Ω = 72.25 W, the internal dissipation will be (4.25)² x 10 Ω =180.625 W.

Now you say "Who told you it is 10 Ω?". The manufacturer said "Not Less than 10 Ω ...". Therefore, whether it is 10 or not is irrelevant at this point for you to argue about it. Suffice it to say that the manufacturer is warning you that the efficiency between dissipated internal power and the delivered power will be less than the designed value. This might lead to a hotter AVR if you reached the 6A: Load will be 6A*6A*4 Ω = 144 W into the exciter and possibly 6A*6A*10 Ω = 360 W being dissipated internally. If not that much, then surely more than the designed value! { suppose internal R = 4 Ohms, then 144W is max at 6A when giving 6A*6A*10 Ω = 360W to load, and eff.=71.4% by design BUT here it will be 50% Only}.

Conclusion: Whatever is the AVR internal R at the Output, by design, the Manufacturer is telling you that if you hooked it to an R < 10 Ω, you loose on efficiency and might exceed the dissipation rating of the AVR. ( No warranty....).

I hope that I was clear enough to dissipate the "Not Correct" Statement...

Reply
Guru
India - Member - Sensors Technology Popular Science - Cosmology - Dream, Think and Act United Kingdom - Member - New Member United States - Member - New Member Canada - Member - New Member

Join Date: Aug 2006
Location: AM-51, Deen Dayal Nagar, Gwalior, Madhya Pradesh, MP 474001, India
Posts: 3418
Good Answers: 32
#7
In reply to #6

Re: AC Generator AVR

10/31/2010 10:51 AM

I think you have done good amount of analysis and you know in details now.

Voltage regulators are often designed with very low internal resistance except that they may trip on over current or over heating.

When warning is for not less than 10 ohms, that clearly means that short circuit protection does not exists or something may get into irreversible change.

For a variable voltage regulator in overload condition and at high preset voltages problems will be worst than what one will see at lower preset voltages. Sometime regulators are meant for high forced currents even at lower voltages down to zero volt as in the case of capacitor changing AVR, then there is full force current at all voltages. However, it all depends on high this device is designed.

I think, warning means real warning, so never one should ignore. AVR without short circuit protection is unimaginable. However there were crow bar like protection that can make some fuse to blow permanently for safety or some PTC or NTC thermistor or resettable or non-resettable fuse to come into action.

Have a look at the circuit manual and perhaps more details may be there to figure out. I am only telling how these circuits are designed and not beyond.

__________________
Prof. (Dr.) Shyam, Managing Director for Sensors Technology Private Limited. Gwalior, MP474001, India.
Reply
Reply to Forum Thread 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); LAA_Lucke (2); redfred (1); Shyam (3)