Calculating Transformer Impedance

10/29/2010 11:23 PM

If you have a transformer name plate which dictates: Isecondary(rated) = 3000A Vsecondary(rated) = 720V Is the transformer impedance not: Z=V/I Z=720/(sqrt(3)) / 3000A Z=.13 ohms?

__________________
Electrical Engineer
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Commentator

Join Date: Jul 2010
Posts: 92
Good Answers: 1
#1

Re: Calculating transformer impedance

10/30/2010 12:09 AM

Also, can someone explain to me how they get the following rule of thumb formula for calculating short circuit power: Short circuit MVA = 100*S / (X%) where S = Rated transformer MVA X% = percentage impedance of the transformer Thanks

__________________
Electrical Engineer
Register to Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#2
In reply to #1

Re: Calculating transformer impedance

10/30/2010 12:53 AM

Excerpt from the webpage : http://www.federalpacific.com/university/transbasics/chapter5.html

The impedance (or resistance to current flow) is important and used to calculate the maximum short circuit current which is needed for sizing, circuit breakers and fuses. Impedance is expressed as a percent. This percentage represents the amount of normal rated primary voltage which must be applied to the transformer to produce full rated load current when the secondary winding is short circuited. The maximum short circuit current that can be obtained from the output of the transformer is limited by the impedance of the transformer and is determined by the multiplying the reciprocal of the impedance timed the full load current . Thus, if a transformer has 5% impedance, the reciprocal of .05 is 20 and maximum short circuit current is 20 times the full load current.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 2)
Associate
Engineering Fields - Electrical Engineering - New Member

Join Date: Jun 2010
Location: IEC Domain
Posts: 43
#3
In reply to #2

Re: Calculating transformer impedance

10/30/2010 10:57 AM

Dear Kvsridhar,

Sir, Excellent website. Quite intriguing and Informative. Keep up the good work. Thank you.

Regards,

DG EE

__________________
The Crazy Man Talks and The Smart Man Understands
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4
In reply to #3

Re: Calculating transformer impedance

10/30/2010 11:14 AM

Glad you liked it

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster
#5
In reply to #4

Re: Calculating transformer impedance

10/30/2010 11:38 AM

Excellent information, but what type of insulation which allows the transformer to run at 220 degree centigrade ?

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: Calculating transformer impedance

10/30/2010 11:53 AM

i am no expert in this field, but Federal says it is Nomex....

You will probably get more information HERE

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply