How to Calculate CFM?

11/01/2010 2:22 AM

please tell me how to do cfm hvac calculation

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Associate

Join Date: Jul 2010
Posts: 50
#1

Re: Enguneering

11/01/2010 3:48 AM

Engun....Eeer it!

Reply
Power-User

Join Date: Mar 2009
Location: United Kingdom
Posts: 308
Good Answers: 28
#2

Re: Enguneering

11/01/2010 7:18 AM

Have you tried that wonderful facility called GOOGLE?

GOOGLE is always my first stop in research.

2nd hit from GOOGLE query "cfm hvac calculation"

http://www.ehow.com/how_5677999_calculate-cfm-hvac.html

Regards Woody

Reply
Anonymous Poster
#3

Re: Enguneering

11/01/2010 7:25 AM

It is generally frowned upon to use a gun for HVAC work. Although if you do, make sure not to over-size or under-size.

Reply Score 1 for Off Topic
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#4

Re: Engineering

11/01/2010 7:38 AM

Air velocity x Cross sectional area of Duct.(appropriate units has to be used)

Reply Score 1 for Off Topic
Power-User

Join Date: Apr 2010
Location: Where no man should ever live
Posts: 195
Good Answers: 6
#5

Re: How to Calculate CFM?

11/03/2010 2:49 AM

You will need a good thermometer.

First, "clock" the gas meter. You do this by running the furnace with the heat on and counting the number of revolutions of the smallest capacity needle on the gas meter over a defined period of time.

You will have to figure out how to convert how many revolutions this needle makes into Btu/hr of gas input. Since it is possible that your local gas company has varied some important parameters of the gas and delivery pressure this may not be conclusive, but it is all you have got. You may have to assume that there is somewhere around 1050 Btu/Cu. Ft. of natural gas.

Since you probably do not have a gas pressure manometer you will also have to assume that the gas pressure in the burner manifold is correct.

If you look at the manufacturer's nameplate on the furnace, it will show the BTU/hr input and probably the output. If the Btu/hr output is not shown multiply the manufacturer's stated input by the presumed efficiency of the machine.

You are trying to get how much gas the furnace used and what the temperature rise across the furnace heat exchanger is. With this information you can calculate the volume of air moving through the furnace using the equation CFM = BTU/Hr Output/ (tout-tin), making assumption that the altitude above sea level at your location is less than 1000 feet so that no altitude correction factor is required.

If you get a Dwyer magnehelic differential air pressure gauge and the right probes you can also measure the pressure drop across the furnace heat exchanger and look up the volume of air moving through the furnace on the manufacture's tables.

This is what they are teaching HVAC technicians today. I have not done either of these 'experiments' yet, but I have seen several furnace installations where incorrectly sized furnaces, read blowers, were installed. I am hoping that when I do come across an installation where the furnace (blower) is incorrectly sized, I am able to determine what the correct sized blower would be. Note that we do not change blowers in furnaces, we install new furnaces.

__________________
Who is so ignorant as not to know that knights-errant are beyond all jurisdiction, their only law their swords, while their charter is their mettle and their will is their decrees? Don Quixote
Reply
Reply to Forum Thread 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Coldspot (1); JCS (1); rakesh_semwal (1); woodygb (1)

Previous in Forum: ASME Sect VIII Div.2 (Material)   Next in Forum: MS Channel Weight Formula

Advertisement