There is fire alarm system already in the building with 28 zones total, 27 used and 1 free. There is space for one more 4-zone module but it looks like it is not possible to get that module any more. Customer is now required to get sprinkler system installed and 6 more zones are needed. The only way other then replacing whole system is to install another fire alarm control with 6 or more zones, tie alarm output of that system to zone on existing system. I see no reason why this would not comply to fire code.
I could monitor both systems separately with cell back up for both and both systems would be located next to each other.
Would anybody know if this configuration could pass fire code in Canada. I know that I should contact local authorities and I am planning to do that but if somebody knows that it will not pass then I would not waste too much time
Thank you very much