Engine Generator Set Load Test

11/02/2010 10:35 AM

hi all,

it is 25 KVA three phase generator, 380v, 38amp, 50hz. we just finished engine overhaul, now i am thinking to do load test to make sure its ok,

now if i will do this, how many amps this set can handle? on the name plate it says that the generator can handle 38amps, can it handle the 38amps or it can not because the engine is not new? and how much the time of the load test should be?

i know this question should be in the mechanical engineering section but maybe one of you guys has an idea.

realy appreciate your help

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Engine Generator Set Load Test

11/02/2010 11:09 AM

The generator specs do not necessarily tell what the engine is capable of. Do you have the kw or hp rating of the engine?

The generator should still be able to handle 38a at 380v and 50Hz, if the engine has sufficient power.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Anonymous Poster
#4
In reply to #1

Re: Engine Generator Set Load Test

11/02/2010 12:18 PM

hi, thanks for your reply

sorry i did not mention this from the bigining, its three piston perkins engine, the mechanic said that its about 25KW.

thanks

Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#2

Re: Engine Generator Set Load Test

11/02/2010 11:32 AM

As Tornado stated, the generator should be able to handle 38A.

A short duration load bank test is 2 hours.

If you do not have a load bank available, run the set on what ever load that you typically back up.

A 1 to 2 hour run should tell you if the engine overhaul was successful.

__________________
The first 5 days after a weekend are always the hardest................................
Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#3

Re: Engine Generator Set Load Test

11/02/2010 11:34 AM

If the engine is after overhaul you should do a progressive test starting with low power and increase it step by step after a short stabilization time at every level. You will notice when the engine is not any more able to maintain the frequency. This will be the limit.

If the engine does not generate a problem then you can increase till the limit of the generator but it has to be known if the values are peak values for short time or values for 100% duty cycle. This should be checked by the temperature or with the coils resistance after every load level.

Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: Engine Generator Set Load Test

11/02/2010 1:58 PM

If the PF is the typical estimated 0.80, this 25kva genset would equate to 20kw electrically. The 25kw engine is a bit more than that, but maybe not enough reserve to start a large load.

If your system consists of a multitude of small loads that can be brought on sequentially, you would probably be okay. If there are any "large" loads, start them first and add the small stuff after.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Engine Generator Set Load Test

11/02/2010 4:03 PM

Basically borrow your Grandma's kettle, Mrs. Browns iron from across the road or anything else you can think of that will take it up to about 30ish amps per phase and see how the engine copes with it.

This is "back yard" testing! No finesse to it, if it works it's OK

__________________
The reports of my death are greatly exaggerated.