11/05/2010 5:25 PM
I want to calculate the Genset sizing for the following 3 phase, 50 C/s, 400/ 440 volts, (1450 RPM, 0.8 Pf) electric motors coupled with Water pumps and controlled by Star/ delta Starters. 60 HP x 4 Nos. + 100 HP x 3 Nos. + 225 HP x 3 Nos. What is the method for calculating the safest load for all these motors to run simultaneously and what cautions should I take in calculating the referred sizing.
Re: Sizing a Diesel Genset
11/05/2010 5:55 PM
Total HP = 1315; for starting the largest motor add 2x225 = 450 for grand total 1765 HP. Convert to KW; 1765 x 0.746 ≈ 1317 KW. Assuming 0.80 PF, 1317/0.80 ≈ 1054 KVA. Select a genset exceeding both of these ratings.
If you can do some power management to ensure that none of the 225-HP motors starts when all the others are running, you can recalculate this by replacing the 2x225 accordingly, which will allow a smaller genset.
Good Answers: 183
11/06/2010 10:29 AM
1317/0.8=1646
and
1317*0.8=1054
Which one do you prefer ?
11/06/2010 1:28 PM
Thank you for catching my error. I see now what I did wrong: I hit "/" on the calculator rather than "*". My fingers don't always go to the right places. 1646 KVA it is.
Good Answers: 244
11/05/2010 8:40 PM
See the earlier thread and the related links for more detail: http://cr4.globalspec.com/thread/58246/Power-Generator-Sizing
- MS
11/06/2010 12:40 AM
Question:
Calculate the GENSET capacity of the following motors.
4 Nos. 60HP = 60*746W = 44.76kW
3 Nos. 100HP = 100*746W = 74.6kW
3 Nos. 225HP = 225*746W = 167.85kW
Solution:
You Total load will be = 44.76*4 + 74.6*3 + 167.85*3
= 179.04 + 223.8 + 503.55
= 906.39kW
When sizing the capacity you need to consider worst case scenarios:-
(1) Running all motors except 1 Nos. 225HP which you plan to start via Y/D.
Genset Capacity = 179.06 + 223.8 + 335.7 + 167.85 * 3 (For Y/D)
= 1.25MW
(2) Running all 225HP motors, 60HP motors and 2 Nos. 100HP motors and you need to start 1 Nos. 100HP motor.
Genset Capacity = 179.06 + 149.2 + 74.6*3 + 505.3
= 1.06MW
(3) Running all 225HP motors, 100HP motors and 3 Nos. 60HP motors, then
Genset Capacity = 505.3 + 223.8 + 134.28 + 44.3*3
= 1MW
Scenario 1 shows maximum capacity so you would choose that. When sizing a Genset don't forget to consider future load as well.
Hope this helps.
Kindly look at MSamad link http://cr4.globalspec.com/thread/58246/Power-Generator-Sizing
11/06/2010 4:13 PM
Thank you all, for your painstaking efforts. Your words improved my knowledge. In future, I will need kind guidance from all of you.
11/06/2010 5:41 AM
Refer EC&M
pnaban