Inverter, Star/Delta, VFD or Soft Starter

11/06/2010 4:01 PM

We have hundreds of 3-phase, 400/440 volts, 50 C/s, 1450 rpm, 0.8 Pf electric motors of SIEMENS origin coupled with 750 to 2500 IGPM Water pumps. All are controlled through Star/delta Starters. Recently, due to increased electricity tariff and other issues, we are considering to replace the star/delta starters with some favorable controlling device like Inverter, VFD or Soft Starter. Someone, expert in this issue may please kindly suggest.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Inverter, Star/Delta, VFD or Soft Starter

11/06/2010 5:56 PM

How do you expect these devices to reduce your utility bill? Are you being billed on a demand?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Inverter, Star/Delta, VFD or Soft Starter

11/06/2010 6:05 PM

There may be some cases in which you could run some pumps at decreased speed and thereby save energy. But there may not be much latitude for this, because if you slow them down too much they might not maintain enough static head.

Soft starters or VFDs may lessen the starting current and eliminate the star-to-delta transients. If it were a new installation VFD's would be a clearer choice; but as a retrofit you'll want to study the economics very closely.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#3

Re: Inverter, Star/Delta, VFD or Soft Starter

11/07/2010 9:55 AM

Soft Starter will not save energy – it is for sure. However, VFD can do it in specific cases of the load characteristics. See the earlier thread for details:

http://cr4.globalspec.com/thread/52637/VFD-vs-Soft-Starter-Pump-Application

I know a case where a VFD marketing person did an experiment showing the energy saving to one of the prospective clients. He first measured the voltage and current of the input of the motor before the installation of VFD. He calculated the power

P = 1.732 x V x I x p.f. (1)

Then he installed the VFD and measured the voltage and input current of the VFD and calculated the power

P = 1.732 x V x I x p.f (2)

He found the current is almost 15% less with the VFD and calculated the consumed power and used the same power factor. He convinced the client indicating that the VFD saves 15% energy.

The tricks that he made here are:

(1) The power factor of the VFD is close to 1, not the power factor of the motor. So, in the second calculation, he should have considered the p.f = 1 in equation (2).

(2) The VFD introduces harmonic current which the ordinary ampere meter is not able to measure. So, the current measured at the VFD input is not included the harmonic components and measured current is less than the actual input current.

Hope it helps.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4
In reply to #3

Re: Inverter, Star/Delta, VFD or Soft Starter

11/08/2010 12:19 PM

GA, but also there is the issue of the fact that a reduction in measured current because of a change in power factor is NOT a reduction in the energy consumed by the load!

Brelvi,

VFDs save energy by matching motor power to load requirements, but at the cost of a few percent in efficiency because of losses in the VFD itself. So the only way the save real energy is if a lot of energy is being wasted in the system and adding the VFD can reduce that waste. If a motor is required to be running at full speed, a VFD is NOT going to save energy in fact it will increase the losses, so it will use MORE energy.

The best savings on VFD applications are only for variable torque (a.k.a. quadratic) loads such as centrifugal pumps and fans, where variable flow is part of the process. Running a motor at reduced speed will consume less energy than running it at full speed and throttling the output for the variable flow requirements. Throttling the output of a pump or fan also reduces the energy used by the square of the flow reduction, but changing the motor speed reduces the energy consumed by the cube of the speed reduction. There is a significant difference in the energy consumed in the middle of those two curves, but not much as either end. So how much you can save is totally dependent on how much load reduction is involved.

Soft starters and Star-Delta starters will not save any energy in the motors. Soft starters help with voltage drop at start-up and torque reduction for mechanical wear and tear avoidance, and they can "soft stop" pumps to help reduce water hammer, but they do not save energy in pumps. Some manufacturers claim so, but those claims are nothing more than "marketing spin" and it is untrue.

Star-Delta should be avoided at all times. It is bad for the motor, bad for the mechanical equipment, bad for the power grid and bad for the control components. The only thing it is good for is reducing initial installed cost because they are slightly cheaper than soft starters.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".