Failure of Single Conductor MV XLPE Cable at Joint

11/19/2010 6:52 PM

We have 4 individual circuits 3 single conductor cables per phase (4 circuits in all) in each cable the Shield and Armour are bonded at both ends to earth and the shields are run to Link boxes with Surge Voltage limiters (the connection here are in Wye)

We have three joints in the cable due to the long run (approx 1.5Km) two joints are simple typical MV joints with Armour and shield joined but separated from each other

The midpoint joint has the source end armour and shield bonded together and the load side similar bonded. These bonds are then run to a Link box conected in Wye

ie A B C from Source C B A to Load and all connected to earth

We are experie3nce serious heating at the armoured connection of the last joint, in fact the temperature is in excess of 110 C, we have two joints that have now failed.

We have circulating current flowing in all three bonds to earth at the load bonding connections (B C A) at the mid point Link Box

It is my belief that isolating the armour from earth at the load end (Transformer) will prevent this circulating current or at least reduce it to a minimum.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Failure of single conductor MV XLPE Cable at Joint

11/19/2010 7:12 PM

Good information for you here and here

Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: Failure of Single Conductor MV XLPE Cable at Joint

11/21/2010 10:58 AM

There is strong magnetic field being produced in this cable. as you are using 4 individual circuits. and because of this there will be voltage drop and heating will take place, and joints will get punctured.

What is the power drawn by these individual circuit. based on the power drawn you have to calculate the type and sqmm of the wire.

Reply
Anonymous Poster
#3

Re: Failure of Single Conductor MV XLPE Cable at Joint

11/21/2010 11:38 AM

What is your system voltage and load

Reply
Anonymous Poster
#4

Re: Failure of Single Conductor MV XLPE Cable at Joint

11/22/2010 9:30 AM

There is a high induced voltage in your armor and or shield relative to the grounds, One of your grounding systems may be generally isolated from other earth grounds. Eliminating the ground at one end can cause hazardous voltages to be present at that point. You need to do a study as to where the voltagew is being induced.

Reply