Failure of Single Conductor 34.5kV XLPE Cable Due to Circulating Current

11/19/2010 7:21 PM

We have 34.5kV single conductor 630mm2 run for approx 1.5Km from SWGR to Xformer (12 cables 4 cirts of 3 cables to 4 Xformers.

WSe have Link Boxes at Source and Xfmr end with Surge Volt Limiters and the Shield and Armoured bonded together and individualy run to the link Boxes

We additionall y haved 3 joints on the run. @ joint are the conventional Raychem type with the Shield and Armour isolated form each other.

The mid point joint has the Armour and the Shield bonded together on both the load side of the joint and the source side of the joint with the load aside and the source side isolated from each other.

These are run to Link Box and connected in WYE to Earth

Although the connections are A B C on one set (load) and C B A on other set (source). We have current in the three connections on the load side and zero on the source side.

Two cables have failed at the armour spring ring at the last joint specifically at the side coming from mid point Link Box.

The other cables have been checked and we are experiencing very high temps at the spring ring at the other final joints

We have attempeted cross bonding at the mid point and have reduced the Circulating current in two phases to a minimum but still have a very high current in one phase.

I believe in isolating the armour bond to earth at the load end as I believe this is what is causing the circulating current to be high.

Any othe solutions????

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Failure of Single conductor 34.5kV XLPE cable due to circulating current

11/19/2010 7:59 PM

Good information for you here and here

Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2010
Posts: 4
#3
In reply to #1

Re: Failure of Single conductor 34.5kV XLPE cable due to circulating current

12/03/2010 1:56 AM

Thank you for your information, although the information from Okonite Cables did not specifically address the problem, it provide information that led to other information and a discussion regarding the cable installation design and ultimately solving the problem

Register to Reply Off Topic (Score 5)
Participant

Join Date: Nov 2010
Posts: 4
#2

Re: Failure of Single Conductor 34.5kV XLPE Cable Due to Circulating Current

12/03/2010 1:52 AM

We found that the problem was due to the armor on the XLPE at the load end (transformer) was earthed through the cable gland, once this was isolated the circulating current which was carried through the shield and found the weakest connection at the joint causing heating up around the tension coil provided in the kit supplied and causing a failure. Subsequent rveiwing of the other joints of the 12 cables (4 separate circuits) show evidence of heating at the joint area. We now have to uncover and inspect the joints a total of 48.

Conclusion is that there are guidelines regarding induced voltages in long run cables and attention as to be paid to circulating currents. Both IEEE and IEC have code guidelines with various options to address these issues.

However design engineers need to be very specific as to what connections must be made and provide detailed drawings for these connections and not leave it up to the cable installation contractor.

Register to Reply Off Topic (Score 5)