11/23/2010 11:32 PM

Dear All,

To what frequency level (Hertz) can we bring down the frequency in a motor to achieve very low RPM,keeping in consideration that the motor doesnt get heated up or fail. Consider the benchmark frequency to be 50 Hz.

Is their any thumb rule for the optimum frequency reduction?

Any special motors?

I have seen in many pharmaceutical plants, reactors/ centriguges where they use VFDs, reduce frequency to achieve low RPM and then also use a gear or change pulley size to further achieve low RPM.

Cant we use only a VFD reduce RPM to the lowest and hence remove the gear or the pulley mechanism.

Waiting for your valuable suggestions.

Kindly help.

Regards,

ROONEY

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Frequency reduction through VFDs

11/23/2010 11:54 PM

In theory some VFDs with some motors are capable of being operated at any speed reduction, right down to zero. There is a lot to it however, not something to be undertaken by amateurs. Do you have anyone local with experience who can look at your application and provide a guaranteed solution? If so, I would highly recommend it as the questions you are asking indicate you may be in over your head.

Here are some very very over simplified ideas though:

Standard motor, standard V/Hz VFD; 4:1 Turn Down Ratio (TDR).

Standard motor, Sensorless Vector Control (SVC) VFD; 6:1 TDR

Basic Inverter Duty air cooled or TENV (not blown) motor, SVC VFD; 10:1 TDR

Good Inverter Duty air cooled or TENV (not blown) motor, SVC VFD; 40:1 TDR

Premium Inverter Duty blown motor, SVC VFD; upwards of 600:1 TDR

Premium Inverter Duty blown motor with encoder, Full Flux Vector VFD; 1000:1 TDR, down to zero speed.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#2

Re: Frequency Reduction Through VFDs

11/24/2010 10:59 PM

Keep in mind that your gear or pulley system reduces speed but INCREASES torque.

If you reduce speed using a VFD you will only get the rated motor torque.

Also, when reducing speed it is best to fit an externally powered fan as an integral fan will not cool the motor adequately.

__________________
johny451
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#5
In reply to #2

Re: Frequency Reduction Through VFDs

11/25/2010 7:12 AM

I think it is the best option as motors at lower frequency to those are wound for continuous duty cycle is not recommended and reduction by gears is the best option.

As for as VFDs are concerned these soft-starters [means from ~zero Hz] and to take the motors to their operating speed in preset time at a linearly rising slope [Hz/Sec].

Register to Reply
Power-User

Join Date: Aug 2008
Location: Melbourne, Australia
Posts: 476
Good Answers: 32
#10
In reply to #2

Re: Frequency Reduction Through VFDs

11/25/2010 5:38 PM

How can this be off topic when he asked:

"Cant we use only a VFD reduce RPM to the lowest and hence remove the gear or the pulley mechanism."

__________________
johny451
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#3

Re: Frequency Reduction Through VFDs

11/24/2010 11:27 PM

The safest slowest speed of any Nema design B motor is 40% rated speed. Be low that, you need to look more closley as to the MFG's lowest speed rating. Like other posters, there is a lot to consider when using VFD's.

__________________
"Real Bass Players" do not use picks
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#4

Re: Frequency Reduction Through VFDs

11/25/2010 6:00 AM

In the constant torque mode you can normally go in the ratio of 10:1.If the operation is likely to be for a longer duration you cannot have a standard fan cooled motor operating at 5Hz as the shaft mounted fan will not be able to give sufficient air.So additional cooling by blowers is required .VFD specially designed motors with built in blowers can be used.It is important to know the duration at each speed while selecting a motor to be used with VFD.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#6

Re: Frequency Reduction Through VFDs

11/25/2010 7:56 AM

If you're looking for slow, controllable rotation, why not look at stepper motors?

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#7

Re: Frequency Reduction Through VFDs

11/25/2010 8:48 AM

another option is use motorised gear units (Geared motors) with VFD if u are looking at very low speed for longer duration.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Anonymous Poster
#8

Re: Frequency Reduction Through VFDs

11/25/2010 12:39 PM

Actually I have an invention that allows to develop a new type of motor at one millionths of rpm. It is free of ferromagnetic materials and its free of all faults of induction motor. Would you like to invest into my invention? Perhaps buy a license to produce it?

contact: kaztechnologies@shaw.ca or tel. +1.778.397.8999

Register to Reply
Anonymous Poster
#9

Re: Frequency Reduction Through VFDs

11/25/2010 12:54 PM

ordinary motor does not run well when frequency lowers below 20 Hz. It become noisy and heats up. What exact rpm do you need? What is the needed torque for that rpm? Do you want it to be light?

I think the very low rpm is easy to achieve with stepper motors that are used in motion controls. You can get one with resolution 1000 steps per full revolution. so the rpm could be 1/100000. if you have proper stepping controls. In addition the precision would be much better than that of reduction gears.

Register to Reply Score 1 for Good Answer
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: