If an RTD is open circuit what will the reading be?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: RTDs

11/23/2010 11:58 PM

Think it through a little.

RTD = Resistance Thermal Device. You are measuring resistance as it changes with temperature. But if the wire breaks, what is the resistance of an open circuit?