Generator is connected to 11kV Switchgear, then I have grid transformer which is also connected to same 11kV switchgear.for exporting the power.
Delta of the transformer is on 11kV side and star earthed on the 132kV side, so during starting there is no earthing in the system,
system is ungrounded system or unearthed system.
Ideal way is to
Provide a earthing transformer with NGR at 11kV switchgear for starting of aux load with the grid.
OR
2. By considering star / star transformer with solidly earthed on 132kV side and NGR earthed on 11kV side.
My question can we provide the earth fault protection for the ungrounded system,
by providing BUS PT with primary star earthed and secondary as grounded wye broken delta transformer with a relay connected across the break along with the shunt resistance.
And do away with the additional equirement of NGR and earthing transformer