11/24/2010 5:42 AM

hello , My name is rajesh , working as protection engineer in india , In 132KV sub-station we had 2 no's of 132KV/33KV transformers of 31.5MVA & 50 MVA rating , for33KV Feeder - sevoiur earth faults ,50 MVA transformer buchloz relay is acting & tripping the 50 MVA transformer .kindly resolve my problem sir

__________________
rajesh
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#1

Re: Failure of Buchloz Relay

11/24/2010 3:00 PM

Sorry, we can't solve your problem for you - only YOU can do that. But we can give you some suggestions what to do:

1. Hire a reputable electrical testing contractor who knows transformers, relays, and HV testing to test the 50MVA transformer and its relay to determine if it is the transformer that has an internal fault or internal gas generation (that's what the Buchholz is designed to detect), or if the relay or some other component in the breaker's tripping scheme is falsely operating.

2. Take steps to reduce the frequency of your severe (I assume that is what you meant) earth faults, such as increased clearing of vegetation near overhead lines, larger insulators and/or guards to prevent animal contacts, better maintenance to clean off contamination that could cause tracking or flashover, etc.

3. Get your facility on a regular program of electrical testing and maintenance to head off (many) problems before they occur.