Sampling 11kva lines

11/26/2010 4:44 AM

Hello,

I want to know whether all the three 11kva lines are ok or not, for this I have to saple the 11kva lines before the transformers.

I really appreciate any help in this regard, Do we have any standard circuit for this or we have to design from basic.

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Sampling 11kva lines

11/26/2010 5:41 AM

Dear student,

first, 11 kV or 11kva ?

please find out a power system book and read it. It covers all topics how to design with calculations.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Nov 2010
Posts: 2
#2
In reply to #1

Re: Sampling 11kva lines

11/26/2010 6:23 AM

Dear Sir,

Its 11KV lines which is input to the transmission transformers, Thanks for the information, if you can send some link I will go thro it.
Or if you have ready circuit, It will help me a lot.

Thank you much

Register to Reply
Anonymous Poster
#3
In reply to #2

Re: Sampling 11kva lines

11/28/2010 1:45 AM

11kV is not considered as transmission lines...It is primary distribution.....what is your question? sampling of 11kV lines??...cut a piece from the line for sample...be careful about smoke from your body

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#4

Re: Sampling 11kva lines

11/30/2010 8:48 AM

Your 11kV distribution lines can be "sampled" using voltage (instrument) transformers with primary rated for your 11kV lines and secondary at 115V. The secondary goes to a meter or a voltage relay, that can indicate whether the circuit is above or below the minimum acceptable level.

http://www.electricityforum.com/products/potential-transformer.htm

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); PeterT (1); tantarshan (1)

Previous in Forum: short circuit ratio(SCR)   Next in Forum: 33 kv substation

Advertisement