Previous in Forum: Oil Type vs Dry Type Transformer   Next in Forum: Three-Phases Motors
Reactor Sizing
11/27/2010 1:02 PM
Dear friends,
what are the parameters required for sizing a reactor?
our company have to hookup a new generator with our existing grid..
Generator rating
Rated POWER 12MW
voltage 6300volts
Rated current 1374.6A
rated frequency 50Hz
synchronous reactance Xd=1.8236 (per unit value)
Transient reactance Xd'=0.1814 (per unit value)
subtransient reactance Xd''=0.1115 (per unit value)
negative phase sequence reactance X2=0.1361 (per unit value)
Zero phase sequence reactance Xo=0.0537 (per unit value)
short circuit ratio 0.61
Now we have to hookup this generator with my existing grid(main busbar) design for 31.5kA short circuit current.. in existing setup, when a short circuit occurs 19kA current flow through this main bus...
i have also calculated some parameter for reactor sizing which are listed below
rated current of reactor=1500A
reactance = 0.1ohms
voltage drop = 137volts
X/R=1
but our consultant company also ask one more parameter which is rate of reactance of reactor. but i dont have any idea abt this parameter.
im a young engineer.. i need ur help... plz describe this parameter and other required parameters.
if u have any link or any thing else abt reactor sizing calculation plzzzzzzzz share with me....
regards
ur needy friend
Re: Reactor sizing
11/28/2010 1:36 AM
what is reactor?......
Re: Reactor sizing
11/28/2010 6:44 AM
What kind of reactors? What you mean with "Reactor". I know Nuclear Reactors.
Re: Reactor sizing
11/28/2010 8:42 AM
check the link http://www.freepatentsonline.com/7078830.pdf
Re: Reactor Sizing
11/28/2010 9:57 PM
This is not a simple answer & the other contributors are way off base. It would take too long to put enough information on this forum to answer your question clearly.
If you can get a copy of the old Westinghouse (now ABB) Transmission & Distribution Reference Handbook it has much information in there that will assist you.
Good Luck.
Murphy was an optimist....
Re: Reactor Sizing
11/29/2010 9:23 AM
Just amplifying what KRW43 said, iirc, a common use of reactors is to reduce fault current in a power distribution system. (I seem to have a vague recollection of them also being used in some motor starters to reduce the motor inrush during starting.) (I wish I wasn't getting old ;-)
Re: Reactor Sizing
11/29/2010 9:28 AM
Thanks a lot my friends, i got my answer.....