Hi Experts, Requesting your assistance in below problem,
Problem: Low Voltage Air Circuit Breaker Tripping (ACB-01)
Problem Description: The low voltage ACB-01 trips on the first start up of the LV Motor-01 (250 kW). On the second start the motor starts without any problem with out tripping any breakers.
Data:
Single Line Distribution as below,
ACB-01 - Feeds Power To - MCCB-01
MCCB-01 - Feeds Power To - Motor Control Centre (MCC)
MCC - Distributes Power On - MCC Busbars
MCCB-02 - Takes Power From - MCC Busbars delivers it to Motor-01 Soft Starter (through Safety Contactors)
Soft Starter - Delivers Power To - Motor-01.
ACB01 - LV ACB is 1000 Amp. rated, 3 pole, NW10H1 with Micrologic 2.0A Protection Unit, Ir = 1, tr = 4, Isd = 10.
MCCB-01 - LV MCCB is 500-1000 Amp. rated, 3 pole, NZM N4-AE1000, Set at Full Operating Range.
MCCB-02 - LV MCCB is 315-630 Amp. rated, 3 pole, NZM N3-AE630, Set at Full Operating Range.
Motor-01 - 250 kW, 415 Volts, 3 Phase, 50 Hz
Distance between ACB-01 and MCCB-01 is about 80 meters.
Distance between MCCB-02 and Motor-01 is about 50 meters.
Pls. let me know if further information required.
Re: Low Voltage Air Circuit Breaker Tripping
11/29/2010 2:39 AM
do the second start first. problem solved.
11/29/2010 9:27 AM
What is the motor driving? Is there some chance the first attempt at a start is easing the second start--like maybe starting to stir up something in a mixer or breaker, or starting some rotation (is the second start attempted while the motor is still rotating (slightly) from the first attempt?)
11/29/2010 2:54 PM
I see a lot of information about which components were used. I see nothing about how these parts were used or any measurements of what is happening. I believe that all proper troubleshooting requires measurements of what is actually happening instead of what you believe should be happening. By making a measurement of the current through your circuit breaker in the initial starting and your second start you can identify if the circuit breaker maybe faulty or just undersized.
11/29/2010 5:08 PM
Hi Guys, The motor is driving a round hollow rotor with the blades inside in it. The motor drives the motor which peels the bark off over the whole length of the log.