Number of Cables Per Phase for 35 MW, 11 kV Rating

11/29/2010 6:23 AM

Hi,

Could sb please convey to me no. of cables per phase required to transmit 35 MW using 11 kV rating of cables ? The size of cables used is of 400 mm2.

Regards,

sks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: No. of cables per phase for 35 MW, 11 kV rating.

11/29/2010 6:27 AM

calculate the current....you already selected the cable size...so you know howmany runs are required.

Register to Reply
Associate

Join Date: Mar 2010
Posts: 33
Good Answers: 2
#2
In reply to #1

Re: No. of cables per phase for 35 MW, 11 kV rating.

11/29/2010 10:52 AM

also on USA Gen sets we calculate and provide cables at 115% fla

__________________
guest
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Number of Cables Per Phase for 35 MW, 11 kV Rating

11/29/2010 6:49 PM

Sauravbabu : where are you located? What is your technical expertise?

The table located here shows a 3 conductor CU cable 400 mm² will carry 530 amps in conduit. 530 amps at 11 kv = 10 MW. Please report back as to how many cables you will need for your project. How long is the cable installation? Will voltage drop be a problem? I am waiting for your response.

Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#4
In reply to #3

Re: Number of Cables Per Phase for 35 MW, 11 kV Rating

11/30/2010 5:00 AM

friend, i am in Nepal, and I am electrical engineer.

Thanks for reply anyway.

Regards,

sks

Register to Reply Off Topic (Score 5)
Participant

Join Date: Jul 2009
Posts: 2
#5

Re: Number of Cables Per Phase for 35 MW, 11 kV Rating

11/30/2010 6:36 AM

Dear Sauravbabu, 35MW at 11kV and 0.8pf would mean 2296A. If you are using 400 Sq.mm Copper cable three core cable then considering current carrying capacity of this cable as 500A then with a cable derating factor of 0.7 minimum 7 runs would be required. If the distance is long then you may have to increase number of runs.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#6
In reply to #5

Re: Number of Cables Per Phase for 35 MW, 11 kV Rating

11/30/2010 2:18 PM

Quote Srinivasu "Dear Sauravbabu, 35MW at 11kV and 0.8pf would mean 2296A. If you are using 400 Sq.mm Copper cable three core cable then considering current carrying capacity of this cable as 500A then with a cable derating factor of 0.7 minimum 7 runs would be required. If the distance is long then you may have to increase number of runs."

If the Load is 2296 amps, why do you need 7 runs? 5 runs would be 2500 amps. Why would you need to derate the cable by 0.70?