Need some advice.
We have an 800 ton condenser water system with redundant twin 800 cooling towers that serves as the heat rejection mechanism for our 800 ton chilled water system. The fans on the towers are VFD controlled and I can operate on just one tower, rolling over to the second if I experience a failure with the first tower. As temperatures get colder, the VFDs slow down the fan or fans to achieve the desired condenser water temperature.
When it gets real cold outside, the fans shut off completely and an automatic bypass valve opens to shunt or bypass the cooling towers, thereby allowing the condenser water to increase back to set point.
Over the past two years, we have experienced 4 failures of the bypass valve and on each occasion the temperature of the condenser water system has increased to the point where the chillers started surging and eventually had to shutdown. The failures of the valve have varied, but the net result has always been the same. On one occasion the servo motor burned out because of heavy drag on the valve. We remedy the drag issue and replaced the actuator (actually increase the torque on the actuator while we at.) On one of the other occasions, the actuator simply got stuck and we were able to cycle it and get it to start working. The other two occasions were due to a board failure. Once the board was replaced, the actuator and valve resumed normal operation.
I am questioning if this is the best design to accomplish the intended function of raising the condenser water temperature and would like to hear your comments and possible alternate design suggestions.
Other pieces of information that might be useful:
* The control valve is a 12" butterfly valve. The valve and actuator are made by Bray Controls (who have a very strong reputation.) We have at least 10 other Bray Control valves on this and other system and none of the them have given us any trouble.
* The valve and actuator are installed outdoors, underneath the cooling towers. The actuator can does have a small heating element inside which is supposed to help prevent condensation. I though about relocating the control valve indoors, but this is not feasible/possible due to the location of the piping and the condenser water pumps (pumps are located outdoors.) I would have to run a 12" line from inside the building to connect to the condenser water pump inlet header (about 75 feet.)
* The most recent failure happened when the temp had dropped to about 25 degrees outside.
* In each failure, the valve has failed open or partially open - which leads to the condenser water not being able to reach the tops of the towers.
I would appreciate any advice on component, configuration or any other helpful suggestions that you might have. Let me know if there are any other pieces of information that you need too.
Thanks.
Regards,
Paul