Slipring Motor Brushes

11/30/2010 5:56 AM

we have a 4mw 6.3kv slipring motor wich has 66brushes on it's rings.(each ring 22 brushes).brushes are of type RC53(METALGRAPHITE).TWO of this motors are used for one mill in plettizing plant.brushes of two motors were decaded (in lenght) after 1400 hours of operation.we replaced brushes by the same type.one motor got normal but the other one it's brushes lenght decaded very fast.we replaced the motor with a motor with the same charactristics .but new motor brushes also were grinded in 48 hours.normally due to maintenance manual of motor and brush 5 mm decade in 1000 hours of operation but our motor uses 20mm in 48 hours!!!.we checked the motor starter resistance and rings are smooth and no arc or spark was seen.operator saies that in 7:30am slipring area was ok. by visual check but in 8:30am the windowes were dark of brush powder!!!! and operator stop the motor by emg.stop.by visual check it seem that brushes are of two type but all of them are marked the same and supplied by the motor supplier.incidentally spare brushes are from 2005 up to now in warehouse,can this have influence brush charactristics.help us on this .tnx in advance

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Oct 2010
Location: Quantum Dimension
Posts: 85
Good Answers: 1
#1

Re: slipring motor brushes

11/30/2010 6:21 AM

Yo Guest,

We experienced something similar on the brushes of the swing generators of P & H draglines.

It was also extensive wear , nothing specific to see or even feel.

I dried the brushes we had in stock , it was high humidity in our case.

Maybe it is something like it at your place as well ?

Good luck T L.

__________________
Humans use 10% of their mind , WE take the rest
Reply
Anonymous Poster
#4
In reply to #1

Re: slipring motor brushes

12/01/2010 5:48 AM

how brushes can be dried?

Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#2

Re: Slipring Motor Brushes

11/30/2010 1:50 PM

Looking at your problem there may be following reasons

1. Holder pressure is too high

I think regarding Holder pressure, it will be OK.

2. Temperature inside Carbon brush compartment is not to the desired value

I think problem is on the temperature of Carbon Brush compartment side. Carbon brush wear increases either the temperature increases/decreases up/down a certain band. e.g normally there is a heater installed inside this compartment to maintain a certain temperature and to control the humidity. In our case (4300 KW, 6300 V, 50 Hz, Y, 457 A, P.F 0.89, 995 RPM) compartment temperature normally remains between 45 -60 C. In either case whether the temperature is below 45 C and above 60 C, wear rate increases

2nd check the ventilation fan (internal cooling fan) is working. Check the filter inside of the compartment are working properly. If air filter are not working normal they are also going to disturb the temperature inside the compartment.

Air regulation is very necessary. either a flow sensor or differential pressure is installed for this purpose. In case of abnormality (air flow)it stop the motor.

We also face the same problem and change the filter and problem get solved.

Please send some information like

1. History of this motor (Before this problem some event)

2. No of Cooling fans

3.Thermostate setting

4. Full nameplate of motor and manufacturer

also what do you mean by this

"we replaced the motor with a motor with the same characteristics .but new motor brushes also were grinded in 48 hours."

Please share with us your finding

Waiting for ur Reply

Reply
Anonymous Poster
#5
In reply to #2

Re: Slipring Motor Brushes

12/01/2010 6:15 AM

1#4000kw 995rpm 6.3kv 442amper rotor voltage 1620 rotor current 1477 p.f.0.86 manuf.by ABB

2# no event before that explaned]

3#no thermostat

we have two mills with same motors we replaced the motor by similar motor of the other mill and new motor had the same behavior in this position

to know:we have ordered a set of RC53 brushes and are going to start motor with new brushes

Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#6
In reply to #5

Re: Slipring Motor Brushes

12/01/2010 9:22 AM

"by visual check it seem that brushes are of two type but all of them are marked the same and supplied by the motor supplier"

Was wear rate same on all brushes

Are both motors are from the same manufacturer?

Reply
Anonymous Poster
#7
In reply to #2

Re: Slipring Motor Brushes

12/03/2010 3:45 AM

hi

we uncoupled both motors of mill and start them with new brushes that were bought recently (yesterday). after 3 hours of working operator stopped the motor because mentioned motor windows were coverd by brush powder.wear rate was very high 8_14 mm in 3 hours .the other motor of mill was normal. we dismantel all parts of brushgear and cables to starter and insulators and.....after checking and washing, parts were reassembled.we start motor and after 12 hours of working behavior was acceptable, know mechanical group is coupling the motors.incidentally motor is air cooled with 3 fans on motor shaft 1#circulation of cooling air in cooling pipes 2#slipring area fan 3# stator area fan also we put pt100 in slipring area and during latest working slipring area temp. was about 24 degrees centigrade.

Reply
Anonymous Poster
#9
In reply to #7

Re: Slipring Motor Brushes

12/06/2010 6:15 AM

Now what is the condition of the motor. Is it now working normal.

Is problem on the motor starter side.

Please Don't forget to tell your experience regarding this problem

Reply
Anonymous Poster
#10
In reply to #9

Re: Slipring Motor Brushes

12/09/2010 5:43 AM

NOW AFTER 100 HOURS OF WORKING MOTORS ARE WORKING NORMALLY AND WEAR RATE IS ACCEPTABLE DUE TO MAINTENANCE MANUAL OF MOTOR.WE THINK THAT DIRTY AND WEAK INSULATORS CAUSES CURRENT LEAKAGE AND THIS WILL PRODUCE HEAT AND HEAT WILL INCREASE WEAR RATE OF BRUSHES.

WAITING FOR UR IDEA....

Reply
Power-User

Join Date: Mar 2010
Location: Islamic Republic of Pakistan
Posts: 124
Good Answers: 14
#11
In reply to #10

Re: Slipring Motor Brushes

12/09/2010 9:33 AM

Thanks for sharing the result and be a part of discussion up to the solution of the problem

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Slipring Motor Brushes

11/30/2010 6:48 PM

What does the motor manufacturer say?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Active Contributor

Join Date: Nov 2007
Location: Scotland
Posts: 20
#8

Re: Slipring Motor Brushes

12/04/2010 4:26 PM

I would suspect that the fault is not in the motor, but in the starter/speed control circuitry. The Guest has stated that they have replaced the suspect motor with a similarly rated motor, and the new motor shows the same problems. I would carry out a thorough check of all the motor, and starter connections, and double check those that were disconnected during the original brush maintenance, to ensure they have been replaced in the correct position. I know a 4Mw motor is a big beast, but if possible, and the motors are running in tandem, with the same control gear, I would look to change over the starting/speed control circuitry, to see if the problem moves to the other motor. This would isolate the problem to either the motor, or control gear.

Reply
Anonymous Poster
#12
In reply to #8

Re: Slipring Motor Brushes

12/10/2010 12:25 AM

hi

we think that it was a mixed problem first bad brushes and then current leakage.at first we checked starter and connections and we have no speed control.