Sizing Pipe or Orifice to Reduce Flow From an Already Water Flow, Existing Pump.

11/30/2010 11:11 AM

getting a new condenser, flow through the condenser needs to be 60m3/h and 120 m3/h max. The cooling water for the condenser will come from our cooling tower water, the pumps have a max flow of 1250m3/h. one pump is running at 45%(562.5 m3/) and the other at 70%(875m3/h). The line i am lookin to come off from is an 8inch line reduced to 6inch and then to 5inch to fit the condenser. i am looking to come of the pump supplying 45% of water, i belive it is only being used on another smaller heat exchanger, i do not know the flow going in.

how do i reduce the cooling water flow to the desired rate (60-120 Max m3/h) without using a flow controller. i have gate valve already placed but thats just a temp solution for regulation of flow. i have been asked to use an orifice plate or size the pipe work acordingly. how do you even work that out, with all the pressure drops, lengths areas it seems like a lame solution.

or is there any other way, also i need calulations so i prove it, im a new engineer with first project so please help

__________________
ChemEng
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Sizing Pipe or Orifice to Reduce Flow From an Already Water Flow, Existing Pump.

11/30/2010 12:47 PM

Use Bernoulli's equation which states that for steady-state flow piezometric pressure (p + gamma * Z) plus velocity head (V*2/2g) are constant between two points.

You don't want this as excess energy for your purpose exists. The plate, flow-throttling, or sudden contractions (due to pipe size reductions) are all methods to cause the flow regime to become "unsteady". The fluid will dissipate fluid energy as heat.

You need to loose significant energy before the fluid enters the heat exchanger.

Another equation needed is continuity Q=VA (not linear for pipes) and only applicable for "steady" flow.

Pick up a hydraulic handbook or tables or grab a nomograph to solve these pipe equations.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Sizing Pipe or Orifice to Reduce Flow From an Already Water Flow, Existing Pump.

11/30/2010 12:47 PM

There are numoreus flow calc softwares such as this: Pipe flow rate calculation | calculate pipe pressure drop with ...

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3

Re: Sizing Pipe or Orifice to Reduce Flow From an Already Water Flow, Existing Pump.

11/30/2010 1:49 PM

We need to know the head vs flow characteristics of the pump, the relative elevations of all the items, any requirement of the condenser for entering water pressure, at least a rough idea of pipe sizes and lengths in the overall system, and any pressure gauge readings that may be available.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
Hobbies - DIY Welding - New Member

Join Date: Apr 2008
Location: Bristol, Tennessee
Posts: 1177
Good Answers: 58
#4

Re: Sizing Pipe or Orifice to Reduce Flow From an Already Water Flow, Existing Pump.

11/30/2010 3:39 PM

Temporarily put a water meter in the line you want to control, and have a pressure gauge at the same location. Measure the flow and pressure for all conditions, to get a handle on your situation. Once you have the numbers for max flow and pressure, you can then use standard tables to determine what size orifice will suit your needs.

If it would not clog up with sediment or scale, you might leave the meter in, so you could tell if flow in the system changes, due to scaling, etc.

__________________
mike k
Register to Reply
Power-User

Join Date: Oct 2010
Location: Indian Mills,Southern N.J.
Posts: 140
Good Answers: 5
#5

Re: Sizing Pipe or Orifice to Reduce Flow From an Already Water Flow, Existing Pump.

12/01/2010 12:56 AM

you can have the impellers machined to pump a lesser value. after you figure out your pipe , fine tune it with the impeller,

__________________
anyone can F--*#@% up a design.It takes a good Man to fix it. Macgyverism at its best.
Register to Reply
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#6

Re: Sizing Pipe or Orifice to Reduce Flow From an Already Water Flow, Existing Pump.

12/01/2010 12:42 PM

You should take several steps to make sure you understand the heat and water flows of the existing cooling water system, and the impacts of the added condensor to the system.

Step one is to make a diagramatic sketch of the system as it now exists. Include any thing you know or can assume for pipe size, flow rate, water temp, and pressure at various system points

Step two is to fill in the heat loads that use the cooling tower capacity, with assumed numbers for heat load, flow rate, and temperatures in and out of the different branch lines.

Third, confirm the pumps and cooling tower do have sufficient capacity to handle the addition of the condensor into the system.

Step four, sketch in the proposed location of the branch supply and return piping for the new condensor. Add in the assumed numbers for heat load, flow rate, and temperatures in and out of the condensor.

Step five is to confirm the new numbers do not compromise existing system operations. If needed iterate with differing flow rates and temperatures to optimize the new system behavior.

Step six, after the desired revised system performance is optimized, begin to size the piping to handle the flow to and from the new condensor. Try to oversize by 10 or 20%, and use butterfly valves at the new condensor to balance and adjust flow as needed.

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Register to Reply
Guru
Popular Science - Evolution - New Member

Join Date: Jul 2006
Location: India-Chennai.
Posts: 722
Good Answers: 30
#7

Re: Sizing Pipe or Orifice to Reduce Flow From an Already Water Flow, Existing Pump.

12/01/2010 11:41 PM

"How do I reduce the cooling water flow to the desired rate"

Your ultimate aim is to ensure the condenser just the required water and not more, right? You have a valve on the line leading to condenser, as you told. Keep pinching this valve until the condenser cries for water. This should be indicated by the rise of vapor pressure in the condenser. Add a little (say a quarter turn or even less) and ensure the vapor pressure get reduced back to desirable value. This, as you fear, is a temporary solution and an orifice equal to the opening of the valve would be a desirable permanent solution, right?

Suggestion1: Try using a Globe (preferably a 'rising spindle type') valve instead Gate valve, since former has a better control on flow for adjustments. Once you have achieved the right amount of opening, lock the spindle at that position such that you can close but not open further. This can be simple done with two nuts to suit to the spindle thread. And nuts are to be fixed below the valve yoke thread.

This can be adjusted whenever wanted, of course, with tools only.

Suggetion2: Arrange a setup as illustrated. On the downstream of the valve locate a suitable flange joint (if not, avail one) for the insertion of orifice. Keep few approximate sized orifices in steps; say 1", 1.25" and 1.5".

Start with the small orifice. Keep the valve at the desired opening. If the installed orifice has the same area of cross section as that of the valve, the pressure gauges PG1 and PG2 should show the same pressure, right? If PG1 is more than PG2, go for the next sized orifice. In couple of attempts you could achieve near precise orifice. Later you could wide open the valve. Take care that the condenser is not starved heavily during this exercise.

__________________
A picture worth thousand words: needless to say if it is animated.
Register to Reply Score 1 for Good Answer
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); darren2264 (1); lyn (1); mike k (1); Ried (1); Tornado (1); yesyen (1)

Previous in Forum: Flow Through Rate of a Gas at a Constant Pressure Leaving an Oriface   Next in Forum: Metallurgists... is There a COR-TEN Steel Sealant?

Advertisement