ETAP 6.0 ARC Flash

12/06/2010 10:45 PM

I am performing the Arc falsh via ETAP 6.0 .

The main Bus also called as Generating side bus where 2x 740 KW generators are connected and feeding the bus showing PPE exceed limit with Incident energy 1.1 cal/cm2 and working diatance 5.75 ft .

Need to know what does it means and how to solve out this problem of PPE exceed limit .

Register to Reply
Pathfinder Tags: ETAP
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: ETAP 6.0 ARC Flash

12/07/2010 2:20 PM
Register to Reply Score 1 for Good Answer
Anonymous Poster
#2

Re: ETAP 6.0 ARC Flash

12/07/2010 11:51 PM

I do not have much info about the whole idea of arc flash and PPE.

I will subscribe to this line of inquiry to learn as much as I can about this "new" hazard that I am exposed to almost daily!

With the machine that we used to build before the "economic turmoil" the higher voltage (480-600V) was separated from the control voltage. I would now consider the control voltage to be set at 24v dc just to minimize the problems with "ARC FLASH"

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#3

Re: ETAP 6.0 ARC Flash

12/08/2010 8:37 PM

Sir,

The reply by Wareagle, with the reference should have helped you a lot. If I understand your data correctly, the software is stating that you have exceeded the 1.1 cal/cm2 minimum energy level at a distance of 5.75 ft. This means that at any distance closer than 5.75 ft you must be wearing appropriate PPE of flame-retardant construction. Since energy is inversely proportional to the square of the distance, you can rather quickly approximate the energy at shorter distances. For example, at 3.0 ft it is (5.75/3.0)2 x 1.1 ≈ 4.1 cal/cm2 (approximately).

I am surprised that the documentation with the ETAP software did not provide this guidance.

--JMM

Register to Reply
Active Contributor

Join Date: Nov 2014
Location: PO Box 746439 City Arvada, State CO
Posts: 12
#5
In reply to #3

Re: ETAP 6.0 ARC Flash

12/22/2014 4:53 AM

An Arc Flash is an electrical explosion due to a fault condition or short circuit when either a phase to ground or phase to phase conductor is connected and current flows through the air.The arc flash blast produces fire, intense light, pressure waves and produces flying shrapnel.Arc Flash can occur, but most of them are human error and preventable.

Arc Flash

Ad Muncher

Register to Reply Off Topic (Score 5)
Anonymous Poster
#4

Re: ETAP 6.0 ARC Flash

12/14/2010 8:30 AM

i think you are using a pirated etap..

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); jmueller (1); martechnical (1); wareagle (1)

Previous in Forum: Electrical protection system   Next in Forum: Potyard

Advertisement