Expertise Needed - Residential Construction Project

12/07/2010 8:42 PM

I am currently involved in a residential construction project in which the owner is doing his own design/build. He is an electrical engineer by training and a career entrepreneur by profession. I am a master plumber by trade and have been providing the benefit of my 30 plus years of experience in commercial and residential construction. The project has been under way since about 2005, starting out as a remodel and developing into what amounts to a completely new 10k plus square foot residence. It's a much longer story, but I digress.

We currently have what seems to be a workable design for the HVAC system. It consists of in-floor radiant heating (16 zones) with air handlers (8 zones) to provide supplemental heat plus humidity control. For cooling, the air handlers will deal with the bulk of the load and the radiant zones will supplement. We have had a considerable amount of design assistance and support from the equipment manufacturers as well as a local mechanical contractor early on. The heat load/gain calculations have been run several times through manual J and ADS and we are pretty comfortable that the piping and duct work which have been installed are more than adequate to do the job. The part we are not comfortable with is actually specifying the particular pumps and valves to be used. One major question we have is whether to use two-way valves with a variable speed pump or a constant speed pump and three-way valves to feed the air handlers. In short we could use some input from an experienced mechanical engineer who might be interested in helping us complete this project.

Note: This is not a community service project. I undersstand I am seeking the input of professional engineers in this forum.

__________________
See Bio for signature line........political correctness and insecure people are such a pain-in-the-ass.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User
Popular Science - Weaponology - New Member Canada - Member -

Join Date: Dec 2006
Location: In the sticks of the Central Kootenays, BC, Canada
Posts: 266
Good Answers: 20
#1

Re: Expertise Needed

12/07/2010 9:32 PM

I'm a ME but HVAC ain't my bag. But your specific question about controlling water flow can be answered in general terms. Especially since the residence is sounding like a fairly high end one where cost isn't that big a deal.

Modern water flow control usually uses variable speed pumps because the energy efficiency is much better. And the flow control is smoother, without any concern with water hammer-which might not be an issue in hydrionic heating, since the pressures are low.

Actually, it seems to me that the pumps and valves (and control system) should be able to be provided to you as a one-stop shop from the same suppliers that have helped you with the rest of the HVAC system. Can't you get these people to spec them?

Jon.

Register to Reply
Power-User
Popular Science - Weaponology - New Member

Join Date: Jan 2006
Location: Fredericksburg, Virginia USA
Posts: 232
Good Answers: 1
#9
In reply to #1

Re: Expertise Needed

12/08/2010 9:36 PM

Thanks for your input. I was leaning towards the variable speed option for the reasons you stated but wasn't quite sure if my conclusions were correct. Most of my experience has been in the commercial end of the construction industry and I have almost always seen air handlers piped with pneumatically controlled 3-way valves so I thought there must be a good reason for it.

Purchasing the pumps and such is following the same basic pattern as the rest of the project in that it is subject to the......idiosyncrasies of the owner who needs to be comfortable that he has learned absolutely everything that he reasonably can about the subject in question before he makes a final decision about anything. This explains why it has taken about 5 times as long to bring this project to it's current state of completion as would normally have been necessary. That said, he is genuinely seeking to do the best job possible within the limits of his budget. Cost actually is a factor, but he tends to spend what is necessary to get it right. What I'm trying to do is find someone with the expertise and the willingness to help us finish out these details so that he is comfortable with the decision. I would prefer someone local but a lot of the collaboration to date has been via telephone and e-mail. That seems to work as well. AutoCAD drawings and any other documentation can be provided in almost bureaucratic quantity if necessary to help the process along.

__________________
See Bio for signature line........political correctness and insecure people are such a pain-in-the-ass.
Register to Reply
Power-User
Popular Science - Weaponology - New Member Canada - Member -

Join Date: Dec 2006
Location: In the sticks of the Central Kootenays, BC, Canada
Posts: 266
Good Answers: 20
#13
In reply to #9

Re: Expertise Needed

12/09/2010 12:04 AM

Well, there must be a phone book full of HVAC engineers in your immediate area, if your owner is willing to spend the money. It sounds like the guy is wanting to understand the design...not necessarily a bad thing. It will mean the HVAC guy will have to do the design and then spend some time explaining it to your client.

Just a thought about the pumping--if I am not mistaken, these hydrionic pumps are usually pretty small-in the 1/8 hp range. During the heating season, at least, if you used constant-speed pumps, the energy lost due to the throttling of flows would be converted to heat, which is what you are dealing with, anyway. And unless you are in an area where electrical rates are heavenly, the payback from the energy saved from a herd of tiny pumps is pretty small.

And thinking about the controls on the zones: Presumably the nice way to set these all would be some sort of central control panel or at least a T-stat in each zone. You had mentioned compressed air controls, which I kind of think may be getting to be a little old school these days--electrical controls lend themselves to computers and night setbacks and all the gadgets that people seem to like nowadays. If you are controlling the humidity as well, then all the more argument for a sophisticated electronic controller. I would suspect you can get electrically controlled water valves for this reason. The controller should also have enough smarts to shut down a zone pump if the heating/cooling load is satisfied for that zone and only restart it when a thermostat calls for heating or cooling.

"Guest" raises a good point, too--if you are cooling a floor there will be some concern that water will condense out of the air onto that cool/cold surface. At least you can control the condensation in the air handlers and route it to a drain. A cold soggy floor wouldn't be too good to impress the house guests with, especially if it has a rug over it! I guess if one is monitoring humidity, then a sophisticated enough controller will be able to decide if "radiant cooling" should not be used if the humidity is too high due to the potential for condensation!

Jon.

Register to Reply
Anonymous Poster
#2

Re: Expertise Needed

12/08/2010 12:39 AM

"For cooling, the air handlers will deal with the bulk of the load and the radiant zones will supplement."

Radiant zones will supplement? How are you going to keep the floor from becoming soaking wet?

________________________

Jesus is DEAD. Praise ALLAH

Register to Reply Off Topic (Score 3)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#3
In reply to #2

Re: Expertise Needed

12/08/2010 6:58 AM

You guys both need to stop using religious references, it only leads to problems.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #3

Re: Expertise Needed

12/08/2010 7:21 AM

I agree. This is no place for it. It just proves their total ignorance and disrespect.

Register to Reply Off Topic (Score 6)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#5
In reply to #4

Re: Expertise Needed

12/08/2010 7:27 AM

I had posted a much worse response to #2, but thought better of it and was able to edit. It would have offended others on here that I don't need to offend.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Off Topic (Score 5)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: Expertise Needed

12/08/2010 8:00 AM

I see what you mean. You couldda gone out in a blaze of glory.............

Register to Reply Off Topic (Score 5)
Power-User
Popular Science - Weaponology - New Member

Join Date: Jan 2006
Location: Fredericksburg, Virginia USA
Posts: 232
Good Answers: 1
#10
In reply to #5

Re: Expertise Needed

12/08/2010 9:45 PM

My aim is not to offend, but merely communicate a little of who I am. I don't hold anyone but myself to my personal standards. Like Popeye though..." I yam what I yam ...aah- g -g -g -g- g".....

__________________
See Bio for signature line........political correctness and insecure people are such a pain-in-the-ass.
Register to Reply Off Topic (Score 5)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#14
In reply to #10

Re: Expertise Needed

12/09/2010 7:59 AM

You should put it in your bio on your profile page. The problem is, when comments pop up like what the guest in post#2 wrote.........I DO get offended, as well as others on here and entire threads can get ugly, fast. I wasn't judging you.....but it is best to keep religious references out of the main forum, as they tend to bring out the crazies from all over the place.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Off Topic (Score 6)
Anonymous Poster
#19
In reply to #14

Re: Expertise Needed

12/09/2010 11:57 AM

The problem is, when comments pop up like what the guest in post#2 wrote.........I DO get offended,

I hope I can assume that you are equally offended by my tag line and Water Buffalo's. One is no more offensive than the other: Both are expressions of untestable beliefs. Mine is at least considered historically accurate by a majority of the earth's inhabitants. For most (about 2/3) of the people on earth, (for Jews, Muslims, Hindus, Buddhists, Jainists, Atheists, and others) Jesus is simply a man -- often considered a great man -- who died, or is outside of consciousness altogether.

Christians are told "Thou shalt love thy neighbour as thyself." Moses did not mean "Love only the person next door." He was referring to all mankind. He spoke of tolerance. (One of the more difficult Buddhist practices for westerners is to meditate on truly loving your enemy: it is easy for westerners to mouth the words "Love thy neighbor" but many find it difficult to wish the Taliban well, despite the Christian need to do so. Interestingly , Buddhists can "walk the walk" of Christianity better than many who publicly advertise themselves to be Christian.)

It is intolerant to impose one's views upon another, and to treat the god or gods of another as somehow less valuable or truthy than ones own gods. It is impolite, at best, to command others to praise your particular Lord. At worst it is no better and no different that the Taliban's insistence on following their own fundamentalist rules.

Commanding others to praise your particular lord does not fit with the core teachings of Moses, Jesus, or Mohammad, (nor, of course, with any of the Buddhist or Hindu teachings.) When we post on CR4 we are "speaking" to Hindus, Jews, Muslims, Buddhists, Atheists, etc., none of whom want to be commanded to Praise the Lord when that lord is defined as Jesus.

Water Buffalo is entitled to his religious belief's, and is entitled, by law, to shout them from street corners in most of the developed world. However, he is not entitled to express them on CR4. He and I are both equally violating the intent of the CR4 guidelines prohibiting religious discussion, because such a one-sided view naturally brings about equal responses presenting other views, and CR4 is not all about religion.

To give equal time to just 10 other possible religious views would mean about 2600 posts with tag lines not unlike mine (to balance Water Buffalo' 260-or-so posts). ("Jesus is dead. Be mindful of many gods." "Jesus is dead. Praise God as revealed in the Torah." ...).

Ironic:

"But thou, when thou prayest, enter into thy closet, and when thou hast shut thy door, pray to thy Father which is in secret; and thy Father which seeth in secret shall reward thee openly."

Jesus did not favor open prayer, especially open prayer done to exalt the speaker. When WB posts his tag line, he does it to exalt WB: to let you about him, "communicate a little of who I am."

they tend to bring out the crazies from all over the place

They also tend to bring out 1. people highly-educated in Christianity, who do not believe in imposing their views on others, 2. Jews who, as a group, have been persecuted by both Christians and Muslims, 3. Muslims who have been persecuted and marginalized by Christians and Jews and Hindus, 4. etc., etc., etc.

____________________

Jesus is dead. Praise Allah

Register to Reply Off Topic (Score 6)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#20
In reply to #19

Re: Expertise Needed

12/09/2010 12:21 PM

Yes, both of your tag lines will offend someone. You should put them in your bio, if anywhere. I'm not discussing this any further.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply Off Topic (Score 5)
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#24
In reply to #19

Re: Expertise Needed

12/09/2010 4:37 PM

It is your right to your religion, your opinions and freedom of speech. It is just that in this forum it is just best too be left out by all. There are other forums for that. Each and every person has their own views, regardless of creed, sect, offshoots of sects, etc.

There are close to 7 Billion people on this planet, and all of them have their own beliefs, faiths, etc. Very few people can totally agree on anything. History and todays events prove that.

I wish to see this forum to stay as a source of information for those who wish to pose and or answer technical based questions, and some times just plain fun, as it was meant to be.

Politics should be other no no. That is even more difficult to avoid.

Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#26
In reply to #24

Re: Expertise Needed

12/09/2010 4:58 PM

There are guidelines here

here's the relevant bit:

Please stay on topic. Posts and comments should be of a technical nature and engage some aspect of engineering, science or technology. If you are going to delve into other topical areas (business, entertainment, sports, etc.), please do your best to tie them back to one of the main focal points of this site. Posts focusing on politics or religion will likely be removed. There are plenty of places on the Web to talk politics or religion This isn't one of them.

I never got a response when I asked how this applied the signature lines

The prohibition on political discussions [or any of the other guidelines] don't actually apply to the GS bloggers.

so preach away, but don't be surprised when the arbitrary moderation starts

Register to Reply Off Topic (Score 5)
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#31
In reply to #26

Re: Expertise Needed

12/09/2010 10:50 PM

Hello Gartth

Did you actually read my full posting or just the first few lines?

If you did read the full posting, than you would have noticed that after affirming one's rights to freedom of religion and free speech, I than went on to state, that there were other forums to discuss it and that this was not the place to do so!

In a way, this was on topic, as the last several posts had slipped down that slippery slope of politics and religion. All I stated was that this forum was for dissemination of technological nature!

You have appeared to ignored all previous direct or indirect religious connotations up until my post, where I suggested that we get back on track to the original intent.

Yes I did read I did read the guidelines when I joined in 2008.

Here's the relevant bit:

Please list, show, expose any posting where I delved into any business , of entertainment, sports, etc. and or even religion that I was involved in, other than a response to another member/ guest, or a request to return to an original thread?

The statement:

"I never got a response when I asked how this applied the signature lines"

I shall be honest, that I do not what you mean by that statement.

But did you ask me directly? The last direct question I received from another member was about my dog.

As for GS bloggers, they hide behind a cloak of anonymity, some are just curious and beginners, some are different. Anyone can play the Great Wizard of OZ (You know, the one behind the curtain).

Preach away; At what? My responses have been either to a direct post. Or to lighten up, or a request to return too the original forum thread?

The Big Question: Did I broach the rules, and how, or other members under the radar for some reason, or are guests allowed free reign?

Please respond!

Register to Reply Off Topic (Score 5)
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#32
In reply to #31

Re: Expertise Needed

12/09/2010 11:41 PM

Maybe resist getting your collective knickers in a twist

The OP should be smart enough to know that such a signature line is just a red flag and will see his thread turned to rubbish.

Relax and watch.

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#34
In reply to #32

Re: Expertise Needed

12/09/2010 11:49 PM

Water Buffalo is a long time member in good standing who sticks to the more practical threads generally

Guests on the other hand are always fair game

along with cigar smoking dogs :D

Register to Reply Off Topic (Score 5)
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#36
In reply to #34

Re: Expertise Needed

12/10/2010 2:57 AM

Ha! Ur guessing - I have mask

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#33
In reply to #31

Re: Expertise Needed

12/09/2010 11:44 PM

Sorry,

my intent was not to pick on you

but to expand on your points, throw up a couple of links

The object of my rant was OBO [our benevolent overlords/moderators] & the lack of any real consistency in these matters

your post was last in line & already marked off topic, when I clicked reply

you in no way broke any "rules"

Again

Sorry for any confusion,

I'll pick on Kramarat next time as he understands my intentions better :D

Register to Reply Off Topic (Score 5)
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#42
In reply to #33

Re: Expertise Needed

12/10/2010 8:38 PM

Point taken, thank you.

Register to Reply Off Topic (Score 5)
Anonymous Poster
#7
In reply to #3

Re: Expertise Needed

12/08/2010 8:05 AM

Well, heck. THERE'S my problem! I was down at the library pouring through various religious tomes and couldn't find a one of 'em with any HVAC formulas or tables in the back.

Besides, everything was in "cubits".

Register to Reply Off Topic (Score 5)
Power-User

Join Date: Feb 2009
Location: TORONTO, CANADA
Posts: 134
#11
In reply to #7

Re: Expertise Needed

12/08/2010 11:25 PM

Yea I laughed, Thanks for the reality check.

__________________
Bin there, done that, then done that again and again and now I forgot where I was.Is this what it means to get old?
Register to Reply Off Topic (Score 5)
Associate

Join Date: Jul 2010
Location: Canton, Ohio
Posts: 30
#16
In reply to #7

Re: Expertise Needed

12/09/2010 8:45 AM

Hey, don't you have to extend your middle finger to accurately measure a cubit ? Oh well, at least it's a quiet gesture for the library.

__________________
"Money talks I know, I heard it once, it said Goodbye”
Register to Reply Off Topic (Score 5)
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#8

Re: Expertise Needed - Residential Construction Project

12/08/2010 11:27 AM

I'm civil not mechanical, but do tons of piping and specify pumps all the time. Here's my 2 cents.

As with most things in engineering there is a give and take. You sacrifice one thing to gain another. The constant/variable speed pump question fits into this. The constant speed pump is a cheaper install, but has a higher operating cost. Operationally either system can be designed to achieve the desired performance as you know, it's just a question of would you rather pay at the front of the project or over its life?

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Feb 2009
Location: TORONTO, CANADA
Posts: 134
#12

Re: Expertise Needed - Residential Construction Project

12/08/2010 11:36 PM

Variable speed controllers are now very popular when even 5 years ago they were exotic and expensive. Today, with good electric motors (high eff.), variable speed drives are cost effective to install even after the fact. (i.e. install on a constant speed motor). The other cost is the control of speed faster/slower depending on expectations this would be more expensive (thermocouples vs temperature switches).

I have often thought that a variable gas furnace would be beneficial in maintaining a more even temp. in my house.

__________________
Bin there, done that, then done that again and again and now I forgot where I was.Is this what it means to get old?
Register to Reply Off Topic (Score 5)
Anonymous Poster
#15

Re: Expertise Needed - Residential Construction Project

12/09/2010 8:36 AM

If the load will not dramatically swing, one way or the other, the two way valves are the way to go.

If the comfort zone temperature and humidity are critical and tight range than the three way would suit you better.

Hope this helps and good luck

Register to Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#17

Re: Expertise Needed - Residential Construction Project

12/09/2010 9:33 AM

I do get involved in Hydronic heating.

1: Get in touch with a plumbing supplier that has a dedicated Hydronic department.

2: Tell them what you want. Have all the information ready to give. Tell them you want a complete package. Boiler, valves, pump, controls, etc.

3: When dealing with multiple zones, check valves are a must.

I would go with the variable speed pump controlling a minimum loop pressure. The three way valves will eliminate the need for manual zone mixing valves.

Register to Reply
Associate

Join Date: Apr 2008
Location: Somewhere near BF, Arizona. ...seriously! ...we're that close.
Posts: 50
Good Answers: 1
#18

Re: Expertise Needed - Residential Construction Project

12/09/2010 9:57 AM

You have indicated that the owner is considering the in floor system to augment cooling. As another poster pointed out, this is just not practical. Floor coverings, the temperature of the floor that must be maintained given the emissivity of the floor's finish, etc and your local climate potentially all conspire against such a cooling solution meeting his expectations.

Having some experience in designing similar systems for industry, and having my own radiant floor heating system in my home in AZ (where we need cooling 9 months out of the year), I dispossessed myself of the floor cooling approach during my design phase. I don't use the radiant floor system for cooling. I would offer the following, but please bear in mind that this response is given assuming radiant floor heating, not cooling:

Without knowing the individual zone run lengths & pressure drops anticipated due to the routing of the (I'm assuming PEX tubing in the floor) this part of your problem seems do-able. The TACO line of pumps for small zone systems (typically 1/2" dia & less than 500' long each) work well for me, but your OP indicates 16 zones. This indicates an industrial sized, but still likely a fractional HP end suction or vertical circulator pump, will likely be needed. There are MANY VFD's available for <$300 that will work up to 2 HP and single phase. Beyond this you could easily go to a 3 phase pump motor, and have the VFD go from the single phase 240 VAC to the 3 phase motor, as these devices typically derive the 3 phase from an internal DC bus anyway. The trick is sizing the pump to be able to handle all the zones flowing at the same time, as well as having sufficient "pump curve" available to handle the significantly reduced flow requirements at the slower RPM. You would want to estimate the amount of time at part load to see if this solution makes sense for your geographic area.

Have you considered that the valves might also be throttling type, 2-way valves that control the water flow on the discharge end of each zone (always best) to an adjustable, but locally set, return temperature? In this case, you could still use the VFD to save the pumping power when the zones are at temp.

You also did not indicate the boiler size and whether it has any special requirements for minimum flow, or whether a main supply & return piping header will be used. Depending on these details I could help you out, but I would like to see a statement of work before committing.

__________________
There are people who make things happen, there are people who watch things happen, and there are people who wonder what happened. To be successful, you need to be a person who makes things happen.. Jim Lovell, NASA Apollo 13 Hero
Register to Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#23
In reply to #18

Re: Expertise Needed - Residential Construction Project

12/09/2010 4:15 PM

There was no mention of in floor cooling, just heating. Water Buffalo is correct to use the air handlers for the AC. This is how I would build my house, just a bit smaller.

The use of two way valves for heating will result in a vary hot section at the start of the zone, as you will be sending in water at what ever temp the boiler loop is. Unless you have a three way mixing valve upstream per zone. Different applications require different temperatures. The air handlers will need a higher temp water than the floor zones. A modulating three way valve controlled by the zone thermostat will provide the correct supply temperature. Note there should be a maximum limit set for all the floor zones.

Register to Reply
Anonymous Poster
#27
In reply to #23

Re: Expertise Needed - Residential Construction Project

12/09/2010 6:44 PM

Someone didn't read the OP closely:

"For cooling, the air handlers will deal with the bulk of the load and the radiant zones will supplement."

Seems that there could be some ambiguity there on a looong stretch, but I took it to indicate an attempt at cooling with the floor...

Register to Reply Off Topic (Score 5)
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#43
In reply to #27

Re: Expertise Needed - Residential Construction Project

12/10/2010 8:42 PM

Opps. My mistake. In floor cooling will be a disaster.

Register to Reply Off Topic (Score 5)
Associate

Join Date: Apr 2008
Location: Somewhere near BF, Arizona. ...seriously! ...we're that close.
Posts: 50
Good Answers: 1
#28
In reply to #23

Re: Expertise Needed - Residential Construction Project

12/09/2010 7:05 PM

Depending upon the layout of the in-floor tubing, supply and return header piping, etc, a "very (sic) hot section at the start of the zone" is not necessarily the case. The fact is that the inlet of each zone will always be warmer than the outlet, or no heat is being transferred into the floor. The VFD system allows the most energy efficiency AND comfort, as the delta T between supply & return headers will decay to some minimum value, as will the pump flow, which will serve to equilibrate the zones. And a warmer zone inlet is not always undesirable; it is often useful. It is common to route the first pass along the periphery for exterior zones where the most heat transfer occurs.

The VFD enables upstream temperature control of a common supply header line via a single mixing point. This system works with the thermostatic 2-way zone valves to keep the return water at the set temperature, and thus control the amount of heat going into the floor in each zone by flow rate and not temperature, per se. This type of system enables greater long term cost savings by reducing, but never completely shutting off each zone.

Putting the proper controls in place allows the boiler to operate at its peak efficiency point, as well as the pump and still achieve cost savings with the VFD while maintaining comfort in the floor heating.

__________________
There are people who make things happen, there are people who watch things happen, and there are people who wonder what happened. To be successful, you need to be a person who makes things happen.. Jim Lovell, NASA Apollo 13 Hero
Register to Reply Score 1 for Good Answer
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#29
In reply to #28

Re: Expertise Needed - Residential Construction Project

12/09/2010 9:00 PM

You have valid points. A properly designed in-floor tubing system is an advantage at the first call for heat. The problem that I see is that your thermostatic return valve is at the exit of the loop. Temperature over shoot can be a problem as the valve only senses the return and not supply temperature.

You mention the single mixing point. The next problem is that you have multiple in floor radiant heating zones, mixed with multiple fan coils. Either system will require different supply temperatures. Also a single zone, like and entrance way can, have very high intermittent demands. The system would have to divert all available hot water to this zone. A central mixing valve will not work, as the pump volume could not compensate for the low water temperature of the mixing valve.

That is unless you have a massive pump and over-sized tubing, or you are running the mixing valve at a very high temperature. This will negate the energy efficiency and still led to very high inlet temperatures to the in floor heating.

It is best that each zone and or device has access to the highest water temperature from the central boiler feed loop. Use a multiple header system off the loop. Three way valves controlled by a zone stat as close to the load as possible is best for control. This will give you both, the capacity and control needed.

Register to Reply
Power-User
Popular Science - Weaponology - New Member

Join Date: Jan 2006
Location: Fredericksburg, Virginia USA
Posts: 232
Good Answers: 1
#30
In reply to #18

Re: Expertise Needed - Residential Construction Project

12/09/2010 10:02 PM

I'm glad to see we're on the right track. At least it appears so from what you posted since we have been over most of those topics repeatedly....except the thing about the 3-phase pumps. We only have single phase available. The system is relatively complex for a residential application but I created a piping schematic to help with the placement of pumps and various valves that would be required. We took the schematic to a local ME and he checked the pipe sizing and flow requirements, and made some notes and comments, but he seemed to think things would work. When we asked him to recommend pumps and valves though, he said we would have to get the manufacturer to to size them. He didn't seem to get the fact that we were looking for him to select a pump or valve that would work in our system and them we could go find a manufacturer with a product to meet the need. I kinda' thought that's what engineers did. The radiant system is going to be tapped off of the loop for the air handlers with it's own pump and tempering valve because it doesn't require either extremely hot or chilled water to function. The air handlers will run with 140F water for heat as opposed to the 103F required for the radiant. The radiant floor disperses the btus over a larger surface area over time whereas the air handlers have to get all the heat into the air quickly from a relatively small coil surface. The cooling side will have a similar difference in temperature with 44F for the air handlers and 59F for the radiant. Humidity is controlled so there should be no condensation on the floors at those temps during the cooling season. There are several comprehensive control systems available but I think we have pretty well settled on a system from Uponor which, I'm told, they adapted from a company called Delta. The Uponor system purports to be able to handle all of the elements we had so far envisioned the system to have. We have the humidifiers on site as well as ERVs and the air handlers and associated ductwork have been nearly completely installed. All the radiant loops have been embedded in the slabs and the manifolds and S&R distribution piping has been run for the radiant system. The S&R for the air handlers is underway, but I don't want to go any further with that until I know exactly what pumps and valving I'm putting in. I find that doing my piping layout is a lot simpler when I know that stuff.

We have been to a couple of local MEs but they didn't seem to interested in this project. I think it's might be due to the unconventional nature of the system and, frankly, the unconventional nature of the client. Most folks in the industry want to do the whole design like they want it and say "here, go buy this stuff and call this guy to install it." They're just not used to clients like my boss. I understand we are not following the typical glide path but we are trying to integrate as much as we practically can of the best modern methods available. That's why we need to find someone who is willing to work a little unconventionally as well.

__________________
See Bio for signature line........political correctness and insecure people are such a pain-in-the-ass.
Register to Reply
Associate

Join Date: Apr 2008
Location: Somewhere near BF, Arizona. ...seriously! ...we're that close.
Posts: 50
Good Answers: 1
#37
In reply to #30

Re: Expertise Needed - Residential Construction Project

12/10/2010 9:31 AM

Hey water buffalo, you're saying all the right things.

It makes sense that most ME's wouldn't want to hassle with finding which zone has the highest DP from which to begin pump sizing calcs.

If you're too far along some of your options may have already been decided, like where to put a pump or pumps. I would need to see your process & instrumentation diagram (P&ID) or piping drawings if you've got them, (or something close to it in the plans?) to avoid buying a small circulator pump, DP gauge (or 2 very accurate pressure gauges), and rising-ball, or rotameter type flow meter and individually testing all loops at their termini for flow rate vs pressure drop. This information is critical to properly sizing the pump for the radiant system. Of course it can be done based on theory, but doing so necessitates a safety margin greater than that of knowing the true system friction head at the design flow rate.

It sounded like you are looking for a single pump and VFD solution. There are killer VFD's out there for the 240 VAC single phase market. Even outstanding quality stuff like this toshiba unit I found on ebay: http://yabe.algebra.com/~ichudov/misc/ebay/Toshiba-5-HP-VFD/ebayhist.html that would be guaranteed to be large enough for your load if the price is right.

Check out this place for great deals on your single phase drives: http://www.driveswarehouse.com/Drives.htm?filter=1&manufacturers_id=10 . Remember in getting a drive that is specifically sized for your load to get a constant torque unit.

From experience, (and as a CEM & installer/operator of similar system as well) I would not want to have to maintain and operate several pumps per system when fewer would do. It has been my experience that the smaller the pumps get, the more often they get replaced, and the lower the overall efficiency. Plus if the system is operating correctly, the water would never be stagnant, for corrosion inhibition considerations, and the fractional current draw of the single pump makes all kinds of sense.

Last thought, again about the floor cooling: Fredericksburg, VA could see ambient dew point temperatures above 59°F and the specifics of the system should be reviewed to ensure the cooling water SP for your floor will be raised in extreme cases to eliminate condensation. Hopefully the structure is designed with sufficient air flow at the floor level to make use of the cool floor surface, either from the AHU's or ceiling fans in every room. We can take any further discussions off line if you like what you hear and want to take it any further.

Otherwise, best of luck.

__________________
There are people who make things happen, there are people who watch things happen, and there are people who wonder what happened. To be successful, you need to be a person who makes things happen.. Jim Lovell, NASA Apollo 13 Hero
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#38
In reply to #30

Re: Expertise Needed - Residential Construction Project

12/10/2010 11:11 AM

Water Buffalo-

There is no need to use 2 temperatures or hot water. The fan-coils can operate with 103F water as well. Just use two coils per AHU for heating and one for cooling (with lower temperature water than being fed through the floor system).

As another consideration- why not use return water from the AHUs to be the water for the floors. you could use, say, 120F water for heating yielding 100-105F return water and 45F water for cooling , yielding 60F return water. The return main from the AHUs could be the supply main for the floors, then the return from the floors could mesh into the return from the AHUs for a final total return connection.

By the way- if you are still looking for someone to help you put this all together, I am willing to donate my time- as long as you know that any designs will not be "stamped".

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#21

Re: Expertise Needed - Residential Construction Project

12/09/2010 2:27 PM

First- I am an engineer who has over 38 years of experience with ALL kinds of HVAC systems, plus I am a Certified Energy Manager.

Based on the relatively extensive zoning that is planned, and the cost of control valves- especially modulating- and their respective control systems, the best, lowest cost and lowest energy usage system is to use individual small circulating pumps for each zone and energize them with line-voltage thermostats.

The pumps will run when there is a call for heat or cooling. When they stop, the amount of residual heat/cool in the coil or floor loop will release lessening amounts of energy. A good anticipating thermostat will account for the residual energy transfer.

Since pump operation will ONLY occur when there is a load present, the pump energy will be the lowest possible- NO background energy use.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#22
In reply to #21

Re: Expertise Needed - Residential Construction Project

12/09/2010 2:55 PM

Would there be a valve with each pump?

In addition you would probably want a central plc to control the boiler, bypass setup. regulate the priority of the zones within the system & any other tricky functionalities that may be desired

Register to Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#25
In reply to #21

Re: Expertise Needed - Residential Construction Project

12/09/2010 4:42 PM

I assume that those pumps have built in check valves?

Register to Reply
Guru

Join Date: Apr 2006
Location: Cincinnati, Ohio, USA
Posts: 662
Good Answers: 49
#39
In reply to #25

Re: Expertise Needed - Residential Construction Project

12/10/2010 11:19 AM

Garth and Icarus-

Each pump is dedicated to one zone, so only a simple balancing valve (with shut-off capabilities) would be required.

Yes, there would need to be a check valve at the connection to the return header.

If "simple, low cost, effective" controls are the goal- it is still a house- the boiler could be controlled by either an outside air thermostat OR a secondary relay activated by any thermostat calling for heat. As stated earlier, each pump would be activated by the zone thermostat. Two solenoid valves- on each of hot and cold water mains- controlled by space thermostat could provide heating / cooling changeover for feed to the pump.

__________________
NO MATTER HOW WELL YOU HAVE DONE SO FAR, ALWAYS TRY TO BE BETTER TOMORROW.
Register to Reply
Anonymous Poster
#35
In reply to #21

Re: Expertise Needed - Residential Construction Project

12/10/2010 12:47 AM

I agree. There are thousands of multi-zone hot water heating systems which function very well without valving.

___________________

CR4 Moderator: Post Modified Politics/Religion: Part of this post was deleted because it was overly religious or political. While each user is entitled to his or her own opinion on these topics, CR4 is not the place for discussion about them. Please review Section 14 of the CR4 Site FAQ and the CR4 Rules of Conduct.

Register to Reply
Anonymous Poster
#40
In reply to #35

Re: Expertise Needed - Residential Construction Project

12/10/2010 1:17 PM

In the post to which this is linked, my tag-line was removed. Although my tag-line said "Praise Allah," the logical equivalent of Water Buffalo's "Praise the LORD," CR4 removed my tag-line but not his. This provides a valuable clarification of the CR4 guidelines. Religious references are OK, but certain words are not OK. With acceptable/unacceptable usage having been demonstrated, the distinctions can now be spelled out in the guidelines. Perhaps this wording could be used:

"Acceptable words for gods are God and LORD. Allah or ALLAH are not acceptable words. While God and Allah are generally understood to refer to the same Abrahamic god, on CR4, it is important to use only the first two usages. On CR4, is is OK to make religious references in every post, if the word LORD is used. For example, see Water Buffalo's posts for acceptable usage. It is not OK to make religious references if the word Allah is used."

This wording could help clarify the CR4 position.

Register to Reply Off Topic (Score 5)
Guru
Popular Science - Cosmology - New Member Engineering Fields - Civil Engineering - New Member Engineering Fields - Nuclear Engineering - New Member United States - Member - New Member

Join Date: Aug 2010
Posts: 714
Good Answers: 38
#41
In reply to #40

Re: Expertise Needed - Residential Construction Project

12/10/2010 1:24 PM

Perhaps CR4 could clear things up by also stating that overtly antagonistic religious remarks or tag lines written by anonymous posters will be removed.

__________________
Sometimes my thoughts are in a degree of order so high even I don't get it...
Register to Reply Off Topic (Score 6)
Anonymous Poster
#44
In reply to #41

Re: Expertise Needed - Residential Construction Project

12/11/2010 1:40 PM

Your point is, of course, well taken. The anonymous poster distinction does not resonate with me, because virtually all members here are effectively anonymous.

I am playing "devil's advocate" (words carefully chosen) here. I have no way of knowing, but suspect that Water Buffalo is not intending to antagonize, even though his posts deliberately go against the CR4 guidelines. I am certainly not intending to antagonize Water Buffalo, but instead am hoping to stimulate the moderators to think about their moderation policy. I know many deeply religious people who find the comment "Praise the LORD" (when the Lord is defined as Jesus) to be somewhat confrontational when posted an explicitly non-religious forum. I know Jews who find it insulting when people (who do not know them to be Jewish) say that they have done "the Christian thing" when they act, as Jews do, with compassion. Other-religious and non-religious members and visitors should not have to put up with being told to praise anyone, let alone a lord or god that has no meaning to them.

When a member deliberately posts religious references on a site that is explicitly non-religious and has rules against religious posts, then those posts are correctly described as antagonistic. This is true no matter what the content: Praise God, Praise the LORD, Praise Allah, Praise Krishna. These are all commands, and as such, are more objectionable than, for example, shalom, salaam, namaste, go in peace, etc. But even the latter probably do not belong here, given the expressed policy.

If CR4 says that this is not the place for religious discussion, but allows one type of religious expression, but not others, then they can only be seen as duplicitous and favoring one religious view over others.

Given that some CR4 members can reasonably be expected to be Hindu, Muslim, Jewish, atheists, etc. they should not be told to "Praise the LORD" when that lord is not their lord, any more than people should be told to Heil Hitler or bow down to David Duke.

On CR4, blatantly religious references should not be tolerated, because they have the potential to offend. (One member in this thread mentioned having been offended by a religious remark: I assume mine, but possibly it was the combination of mine and Water Buffalo's.)

Register to Reply Off Topic (Score 5)
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#45
In reply to #44

Re: Expertise Needed - Residential Construction Project

12/11/2010 5:16 PM

You seem to not know that most deities are titled "Lord" in some way by their followers. So really the only point you have is "the CR4 guidelines". You will note the signature has been changed, grudgingly, but I imagine mostly, so prats stop clogging up threads with off topic parochial "playing with themselves".

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Off Topic (Score 5)
Anonymous Poster
#46
In reply to #45

Re: Expertise Needed - Residential Construction Project

12/12/2010 11:40 AM

You seem to not know that most deities are titled "Lord" in some way by their followers.

I don't know what would lead you to think that. That fact that is central to my point: Praise the Lord (or Praise the LORD, as WB wrote) is a religious statement. If I thought he was meaning praise the lord of the manor, then I would not have taken it as a religious statement.

So really the only point you have is "the CR4 guidelines".

Yes, that is the only point I am making. In environments in which religious statements are not discouraged, I am (and many people are) not just accepting but appreciative of those statements. This is not such an environment, and if CR4 moderation acts in favor of one religion (by saying nothing about WB's tagline) and against another (by removing my tagline) then CR4 is saying that there is something wrong with those who use the term Allah (most of whom are Muslim.) In my view, the last thing the world needs is additional pitting of one religious view against another. This is not playing with myself: many of us know people who have been killed for their religious beliefs.

The people who react negatively to the N word are not a bunch of over-sensitive PC-obsessed droids.

Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#47
In reply to #46

Re: Expertise Needed - Residential Construction Project

12/12/2010 1:48 PM

As an Anonymous Coward [guest] you don't have a signature, only post, your post was moderated.

Membership has it's privileges

I don't believe that Water Buffalo was forced to change his signature line [he did put up a nice new avatar]. He responded to peer pressure

I generally think that the prohibitions on religion/politics are not actually applied consistently & are meaningless/confusing

There have been some new members recently that would post religious diatribes in response to any thread, these members are abusive enough, that their tenure is short lived.

this community should be more open not less. OBO [our benevolent overlords] have in most cases let it rip, only stepping in when the flame wars get too nasty. The official position is to satisfy the legal department, more than an actual set of official rules, which you may notice don't exist, just suggestions....

Register to Reply Off Topic (Score 5)
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#48
In reply to #47

Re: Expertise Needed - Residential Construction Project

12/12/2010 3:12 PM

I agree with you, that openness should be promoted. With that comes the responsibility of the participants of this site to act like the educated, knowledgeable and experienced adults that we are supposed to be.

(Note: Education and knowledge can come from any means. Formal/ in formal education, self taut, done it their whole life, osmosis or just plain willing to learn). I will never dismiss a persons knowledge due to a lack of a piece of paper.

That said, it is up to all off us to show some form of decorum when we post. The powers that be, should not have to step in and moderate.

All involved in this forum realise that we are not just talking to the person next door, but to people around the world. Everybody is different.

We should still ask and debate questions, sometimes we will tickle the Dragons Tail.

Forethought too any post and answer should always be be considered.

As for the guests who like to snipe away from behind the curtain, just sign up! Even behind our avatars and our blog names, we are not totally anonymous. People can and have contacted directly via that option in CR4. Also if we really turn into total idiots, we can be dumped.

So if we are willing to walk the walk, than why not you!

P.S: Was that a little to over the top?

Register to Reply Off Topic (Score 5)
Register to Reply 48 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

34point5 (3); Anonymous Poster (9); ChaoticIntellect (2); energygod (3); Garthh (5); Icarus (9); kramarat (4); lyn (2); MIKE L. (2); Qwack (1); sawmilleng (2); Tucson Don (3); water buffalo (3)

Previous in Forum: Copper Flanges - Pressure/Temperature Chart   Next in Forum: Pump Alignment
You might be interested in: Air Handlers, Radiant Heater Elements, Gas Valves

Advertisement