Dear sir,
I need some information related to voltage drop in burried cable. we choose the cable 0.6 1kv- 3x240mm2 xlpe. maximum ampere requirement is 410.volatage rating 400v. distance is 300 meter.pls let me know the calculation method and % value.
jayan
Re: cable sizing and voltage drop
12/09/2010 6:09 AM
→ British Standard 7671.
Anonymous Poster
12/09/2010 7:36 AM
are we asking for any standard? hope u can understnd english..
12/09/2010 7:42 AM
→ British Standard 7671! <sigh>
Good Answers: 181
Re: Cable Sizing and Voltage Drop
12/09/2010 2:21 PM
BS7671 will give you the answer
Good Answers: 170
12/10/2010 9:39 AM
Please refer to IS 1255. It lists the maximum permissible voltage drop per ampere per km for various sizes & types of cables. From the table given in the Standard, calculate the actual voltage drop for your cable type, size, length & amperage.
The maximum permissible voltage drop at motor terminals during steady state is 6% (as per IS 325) and during acceleration state is 15%. Check if your actual voltage drop fall swithin the above limits. If not, choose the next higher size cable and re-check.
12/14/2010 5:34 AM
Dear Mr.Devutti,
Please visit the following site www.simplified office software.com .
There you will get a ready-rockener for Voltage Drops / Sizes of cables etc. It is
very useful.
Manroop.Chennai.
12/20/2010 4:27 AM
Voltage drop on cables depend on various factor like resistance, Reactance of cable, number of runs and power factor, length of cable etc. The formula for the same is Voltage drop = rt 3xIxLx(Rcos(phi) + Xsin(phi))/no of runs. Hope this meets your requirement