Suppose vendor is submitting the type test report for battry having rating higher or lower than the rating mentioned in data sheet. Is it acceptable or not ? what is the Technical reason for that if acceptable?
Anand Kathale
Re: Type test Report of Battery
12/10/2010 6:01 AM
Does the type test document relate to either the part number or the serial number series of the battery? If so, then what is there not to accept <rhetorical question>?
The purchaser needs to evaluate whether or not it is worth faffing-around with paperwork instead of concentrating on the economic driver of getting this particular battery into service.
India - Member - New Member
12/10/2010 6:10 AM
What does Purchase Order document calls for?
Accepting or not accepting should be as per it.
Some time PO calls for vendor to submit type test certificate of battery of same or higher capacity to be submitted by vendor, which is acceptable to owner. check your case.
When was last time you did something for first time.
Re: Type Test Report of Battery
12/10/2010 12:29 PM
For the acceptance of battery one has to essentially carry out battery charge-discharge test at site which is a standard commissioning function, no one depends on documentation.
Knowledge sharing is a WIN-WIN situation