Selection of NGR for Industrial MV Network

12/11/2010 5:54 AM

1.a What factors to be considered for selecting value of resistance of NGR for MV industrial 6.6 KV and 11 KV Network.

1.b What would be effect on selection if the 6.6 KV network is feed from 11 KV system throug Dyn11 transformer.

__________________
When was last time you did something for first time.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: Selection of NGR for Industrial MV network

12/11/2010 9:45 AM

NGR is to limit the ground fault current, which is to be designed for 2 times of the generator rated current.

Hence the calculation will be as below

Generator full load current x 2 / generator voltage

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#2
In reply to #1

Re: Selection of NGR for Industrial MV network

12/11/2010 11:10 AM

It is not always the case

__________________
When was last time you did something for first time.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: Selection of NGR for Industrial MV Network

12/11/2010 4:06 PM

1a i) If you have zero resistance, current in fault is high (news! MAD arc welder escapes!), -but fuses will blow quick so time is short. But breaker will take fixed time to open, even though relay detection time is short. One phase will lose voltage, this will affect all loads in system. ii) If you have very high resistance, detection relay and current transformers [CTs]will not be able to resolve the small abnormal residual current, hence not possible to trip-off only faulted circuit. e.g. 500 amp circuit breaker with 500 amp CTs and only 5 amp earth fault current due to NGR. All circuits will have to be tripped by relay on NGR. But it was only a 5 amp arc welder, and little damage was done! All circuits will be disconnected, yet again. when you close the breaker back on the faulty circuit. iii) If you have medium resistance, current is enough to detect faulted circuit reliably, only faulted load is disconnected, other loads keep going. Industry happy, except one on faulty circuit! iv) If neutral grounding is via transformer, its ratio will have great effect on actual resistance used! Question asks about "value of resistance" does it not?? 1b Strange question. Compared to what arrangement?? Not defined in Question 1a which suggests both 6k6 and 11k have own NGR. A Dyn (note the n!) has a neutral on 6k6 side, so NGR can be connected from that to ground

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Selection of NGR for Industrial MV Network

12/12/2010 11:09 AM

1a) The one and only factor is the amount of earth fault that you "want" to limit to. NGR value is: Phase Voltage / Desired earth Fault Current. If you keep the value too low, detection becomes difficult and if you keep too large, damages due to the high fault current woiuld be more. If you have rotating machines at the distribution voltage, then better to limit the earth fault current to a value less than the core damage current value (given by the rotating equipment manufacturer in the form of a core damage curve; a typicl value would be about 25A for 1 sec.).

1b) Dyn 11 means your 11kV Side is delta connected and as such you wouldn't have a neutral to earth. But, still if you want to earth the 11kV Side, you may still do so, by creating an "artificial" neutral using a "zig-zag" transformer with the NGR connected to the neutral of this zig-zag transformer. For your 6.6kV side, anyhow, you will have a neutral and you may connect your NGR, considering what is said in 1 a) above.

Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#5
In reply to #4

Re: Selection of NGR for Industrial MV Network

12/12/2010 12:06 PM

let me add to question.

The there are 03 voltage level in industry viz. 33 KV, 11 KV and 6.6 KV

The step-down transformers are used Dyn from 33 to 11 and from 11 to 6.6.

Now there is neutral on 11 as well as 6.6 KV level.

1. What shall be value for NGR for 11KV and 6.6 KV

2. Assuming earth fault current is limited to 30 Amps for 11 KV and 25 amps for 6.6 KV. What would be its effect on protective relay co-ordination.

__________________
When was last time you did something for first time.
Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #5

Re: Selection of NGR for Industrial MV Network

12/13/2010 6:19 AM

Ref. 1 -- both e-e-65 and I have told you the relevant design thoughts. There is no rulebook that covers every case! Without numbers, like the current ratings of the circuit breakers or CTs, one cannot decide the lowest earth fault current which can be detected by a relay. Without that, one cannot calculate maximum resistance for NER. Usually breakers come with CTs rated equal to the CB rating. Ref. 2 -- Co-ordination between which relays?? Between earth fault relays on outgoing breakers and back-up relay on NER?? If question means between 11 kV and 6k6 earth fault relays, there is no co-ordination between them because they are galvanically separate and a Dy transfo will not transfer any earth current back from 6k6. Think where a current in just one of the y windings must go in the D (transfos are reversible). The y coil is wound over or side by side with one phase of the D coils. An earth current on y side ends up as phase to phase current on D side. Which current is the "it" having "its effect on protect...", the 30 amp or the 25 amp?? Until one has a system drawing with circuit, relay locations/settings/delay curves and some current and impedance values discrimination cannot be considered.

Register to Reply Good Answer (Score 2)
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

67model (2); Anonymous Poster (1); electricalexpert65 (1); Happy singh (2)

Previous in Forum: HT Cabling   Next in Forum: Regarding 5 HP Motor

Advertisement