Regarding 5 HP Motor

12/11/2010 7:47 AM

Dear Sir,

I have a 5 HP submersible pump in a bore well, how much power in units it will consume if I run it for one hour daily ? Power rate/per unit is a Rs 6/- per unit in my area.

Regards,

subash sanan

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: regarding 5 HP motor

12/11/2010 8:14 AM

Let's see.

Maximum power 5hp which is, er, 3.8kW, multiplied by 1 h per day is 3.8kWh per day then multiply by Rs 6/- per unit is, er, oh, er, about no more than about Rs 23/- per day.

Deal or no deal?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#3
In reply to #1

Re: regarding 5 HP motor

12/11/2010 1:53 PM

I just cannot resist dotting some i's and crossing some t's sometimes.

Actually most motors are rated in the amount of shaft power the deliver and not the electric power they draw. A likely high but not unreasonable additional 5-10% should be added to put this at about 4-4.2kW. This is the power drawn by this motor at a full load. Now the OP added a time factor of running this for an hour. 4.2kWh is the energy that this motor draws with one hour of constant use. Most electricity utilities charge for the total energy an individual consumes over a preset (monthly) amount of time.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#5
In reply to #3

Re: regarding 5 HP motor

12/12/2010 7:20 AM

Good point well made. Motor efficiency is normally about 85-90% as you imply.

Also, it should be noted that the motor will only consume output shaft demand, so if the pump onl;y requires half power, the motor only consumes half power (roughly, less losses etc), so the 4.2kW/hour maight be 2.1kW/hour in this example.

I suppose its unlikely to be at (or near) full load reducing the efficiency a lttle and power factor much more so.

There are many examples of solar powerred irrigation pumps in use in Spain using VFD technology, BTW.

__________________
Something new every day!
Register to Reply Good Answer (Score 2)
Anonymous Poster
#2

Re: regarding 5 HP motor

12/11/2010 9:44 AM

For one month 23x30=690, an year 690X12=8000, try solar with 2kvar capacitor.

Register to Reply
Guru

Join Date: Jun 2008
Location: Oman
Posts: 612
Good Answers: 14
#4

Re: Regarding 5 HP Motor

12/11/2010 11:59 PM

If it is for agriculture purpose in India at different states there are different tariffs please check it before arrive any final figure. Calculation of power consumption is explained by PWSlack.

Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); MalcolmK (1); mrswamy (1); PWSlack (1); redfred (1)

Previous in Forum: Selection of NGR for Industrial MV Network   Next in Forum: Burnt 34.5 KV Cables

Advertisement