The company I work for has the following distribution system.
Power is generated via 3 diesel driven engine generators. Each generator is rated 2MW, 3 phase, 380 volts output, 60 HZ. Then, stepped up to 34.5KV transformers. After that in a main substation, through 34.5 KV, 3 phase, 60 HZ, SF6 GIS switch gear, power is distributed to other remote unit substations.
From main substation 34,5 KV underground cables are connected to unit substations. At the unit substations, there are 10 step down transformers, 3 MVA each, 34.5 KV / 380V, 60 HZ, 3 phase, Delta Wye connection (Dyn11). This is secondary selective system with 100% redundancy. The demand load for this company is max. 4 MW.
The whole distribution system was energized since September 2010. For test commissioning stage. The total actual load is 1.6 MW. Because we don't need so far the 3 generators to operate in synchronization, one generator is enough to supply this 1.6 MW load. This connected load type is Motors, fans, lights, etc. . Generator # 1 is operating for one week. Then, it's switched off. After that, within 15 minutes generator # 2 takes over. Then, after one week, generator # 3 operates and so on.
Four weeks ago, we have experienced phase#3 (L3) cable got damaged / burnt on the termination side of 34.5 KV. It happened to 4 transformers. Cable terminations were repaired and transformers were back in service. We used the standard raychem type of termination kit for 34.5 KV level. The same type for all our cable termination kits.
Last week, we experienced the same problem in phase# 2 (L2), in a different transformer than the previous ones.
Can you please explain why this is happening and what could be the root cause and how to "resolve" this problem.
Thanks & Regards