12/13/2010 7:23 AM

I need to recall the mathod for calculation and distribution of loads on a DB. I need to recall the standard ratings given to various loads - including lighting and other power loads so that I can calculate the current rating of my DB. Any other fundamental information will be appreciated.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: How to distribute loads on DB

12/13/2010 7:42 AM

Recall ...recall all your mathods and standard ratings. No more fundamental information with me.

Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#2

Re: How to distribute loads on DB

12/13/2010 8:06 AM

Surely you don't expect much of an answer to your question with so little detail, do you? What is a DB (Distribution Board?)? Is this for a home, an industrial or commercial site, other? What other power loads do you have?

Reply
Anonymous Poster
#3

Re: How to distribute loads on DB

12/13/2010 8:31 AM

Draw it in CAD, take a plot, do it.

Reply
Active Contributor

Join Date: Dec 2010
Posts: 12
#4

Re: How to Distribute Loads on DB

12/13/2010 9:00 AM

List out connected loads to be connected on DB. Connect the Load to DB equally if it is single phase Load on all 3 phases.Always maintain Balance Load on all 3 phases.Remaining rating of DB ,I think you are aware of It.

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#5

Re: How to Distribute Loads on DB

12/14/2010 12:46 AM

There are tables giving standard ratings for various loads like lighting-100W,receptacle-90VA etc. Then you should apply diversity and load factors.If you know the actual loads connected you will get very accurate results. The loads should be divided into various circuits(branches)with suitably rated MCB/Cables for each circuit. Making an allowance for future extension you can size the main breaker. Refer BS7671/NEMA/NEC/VDE etc

__________________
pnaban
Reply
Anonymous Poster
#6
In reply to #5

Re: How to Distribute Loads on DB

12/14/2010 3:08 AM

where can I get those tables?...what is load factor?

Reply
Active Contributor

Join Date: Dec 2010
Posts: 12
#7
In reply to #6

Re: How to Distribute Loads on DB

12/14/2010 11:13 AM

You can get tables from electrical items OEM.Load factor=The ratio of average load to Peak load or total capacity of load