Anonymous Poster

DP type Flow TX -N2 line..flow problem

12/14/2010 10:11 AM

hi all, i have DP type flow multivariable transmitter fieldbus foundation using on nitrogen line line pressure 10.55 kg/cm2 & line tempreture 29.98c, but flow showing 0.000 i check all thing orifice is proper install,also checked by close LP&HP block valve so got sensor error.after reconnecting..pressure ok..bt flow same 0...any body have an idea ....

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: DP type Flow TX -N2 line..flow problem

12/14/2010 10:21 AM

Is there any flow?

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Anonymous Poster
#3
In reply to #1

Re: DP type Flow TX -N2 line..flow problem

12/15/2010 11:23 AM

not sure ..so i open next to flow tx one drain valve & purged nitrogen but still result same ,,actually i have same doubt about flow is ongoing or not so i just open drain valve of main line of n2.

when i close both lp&hp isolation valve then i some little bit flow indication like 2.6,,,3.56,,,,,,but once i open both hp&lp and when close equiliser valve so once more flow 0.0000

Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#2

Re: DP type Flow TX -N2 line..flow problem

12/14/2010 5:24 PM

What is the DP? Is the equalizing valve closed? If it's open, DP = 0, flow = 0.

Reply
Power-User

Join Date: Nov 2009
Posts: 335
Good Answers: 63
#4

Re: DP type Flow TX -N2 line..flow problem

12/15/2010 1:05 PM

Did this multivariable ever work properly or is this a commissioning issue?

> so i just open drain valve of main line of n2.

When you opened the main line drain valve, did Nitrogen flow at a high rate?
Did the multivariable transmitter recognize that high flow rate?

Reply
Anonymous Poster
#5
In reply to #4

Re: DP type Flow TX -N2 line..flow problem

12/17/2010 2:24 AM

When you ask us about something pls write in detail....u didnt mention ur required flow.

Check-

1. Equilizer valve in manifold is open or close......close it.

2.Confirm that there is a flow in the line

3.If 1& 2 are ok. Check that whether parameters are set properly in the transmitters.

4.check that transmitter is able to measure ur required flow or not.In range.

5.If the transmitter displays massflow ..then concerned parameters to be set.without it it wont work.

Reply