High Turbine Exhaust Pressure

12/16/2010 9:09 AM

hello guys, i have a problem in my working area.

We have a Steam turbine of back pressure cum condensing type. for moving turbine very high pressure steam is using and two nos. of extraction 1 at high pressure and 2 at lower pressure taken out. after that remaining we get as exhaust. which condensed in condenser for maintaining vaccum. also a ejector system attached with it.

Now a days we are getting problem related to higher pressure of exhaust even all other parameters are same.like as steam consumption, cooling water temp. quantity of condensate etc.

one more finding that the exhaust condenser having tube leakage in which condensing media is cooling water. which also deteriorating condensate quality.

So please suggest what could be the probable reasons for higher exhaust pressure.

** motive steam for ejector system also having same pressure as earlier.

__________________
Manoj Kumar Agarwal
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: High Turbine Exhaust Pressure

12/16/2010 10:12 AM

<...what could be the probable reasons for higher exhaust pressure...>

Here it is:

<...exhaust condenser having tube leakage in which condensing media is cooling water. which also deteriorating condensate quality...>

The condensate is at partial vacuum. The cooling water is at a pressure above atmospheric. The fact that pressure is high and condensate quality is poor indicates the solution to the problem: fix the leaks in the exhaust condenser.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 3)
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#2
In reply to #1

Re: High Turbine Exhaust Pressure

12/16/2010 1:01 PM

I couldn't give the OP a GA for supplying the answer, so here you go.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #2

Re: High Turbine Exhaust Pressure

01/03/2011 8:09 AM

Aw, shucks.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Popular Science - Evolution - New Member

Join Date: Jul 2006
Location: India-Chennai.
Posts: 722
Good Answers: 30
#3
In reply to #1

Re: High Turbine Exhaust Pressure

12/16/2010 11:13 PM

"The condensate is at partial vacuum. The cooling water is at a pressure above atmospheric."

Well said, cooling water getting into steam side of condenser would decrease the efficiency of condenser, thereby the exhaust pressure would naturally rise. Yes, as suggested, fix the leak by plugging the tube or preferably re-tubing the Leakey tubes.

__________________
A picture worth thousand words: needless to say if it is animated.
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Feb 2010
Posts: 87
Good Answers: 7
#6
In reply to #3

Re: High Turbine Exhaust Pressure

12/18/2010 1:50 AM

Actually fluid leaking in wouldn't decrease the condenser efficiency, it would increase the efficiency because it would bring the temperature closer to cooling water inlet temp (lower) which would improve vacuum, not degrade it.

Boiler level increases and carry over and turbine damage would be the heartbreak there....or possibly severe (catostrophic?) corrossion problems if chemestry were left unchecked and coolingwater was less than pristine.

The problem the conditions are pointing to is one of air being drawn into the condenser. That is the reason vacuum is diminishing.

Flee to me remote elf.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #6

Re: High Turbine Exhaust Pressure

01/04/2011 10:48 AM

....which is absolutely fine, except for two things:

  • The OP hasn't mentioned air leaking in
  • This particular hypothesis disregards the OP's claimed deterioration in condensate quality
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Feb 2010
Posts: 87
Good Answers: 7
#9
In reply to #8

Re: High Turbine Exhaust Pressure

01/04/2011 12:04 PM

Pwslack...

The OP hasn't mentioned air leaking in, but then again the OP is asking what might be causing the problem, so if they are uncertain of the answer, we shouldn't judge too harshly if they don't specify the exact answer when posting the question.

Degradation in quality of condensate does not, in any way, disprove that air leaking in is the likely cause of loss of vacuum...

There may be both chill water and air being drawn into the condenser, but the air would still be the cause of vacuum degradation.

Alternately just air might be leaking in to the condenser. Depending on the specific steam plant chemistry, and the plant condition, degradation in condensate quality could be seen fairly quickly as a result of air introduced.

The real kicker here is that water alone leaking into the condenser would actually have a tendency to improve vacuum initially. The reduced temperature, from direct mixing, would mean lower pressure. The condensate pumps will not discriminate against the water that has leaked into the condenser. It will be pumped out with the condensate. it certainly won't get stuck somehow filling up the condenser.

Fluid leaking in is far more likely to be noticed first in boiler chemistry, or perhaps high boiler level, or carry over. It certainly is not indicated nor would it directly cause slow loss of vaccuum.

If you still disagree, please explain what you believe is happening to the contrary.

Register to Reply
Anonymous Poster
#4

Re: High Turbine Exhaust Pressure

12/16/2010 11:32 PM

all the parameters are showing previous values is in't it.....so the problem is from cooling water side only.....cooling water pressure flowing in the tubes is more( above atm pressure) than the exhaust steam pressure......hence the cooling water leaks into the steam side...and finally exhaust pressure or vaccum drops.......and also check for the conductivity in the hotwell......and the cw pupms dischare pressure........

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Feb 2010
Posts: 87
Good Answers: 7
#5

Re: High Turbine Exhaust Pressure

12/18/2010 1:34 AM

I don't know how clean your cooling water supply is, but it would have to be amazingly clean for loss of vacuum to be the primary indication of cooling water leaking into the condenser.

Chemistry should be screaming at you before changes in vacuum if you are drawing cooling water.

you are losing vacuum because air is leaking into the condenser. The air of course doesn't condense and is overwhelming the eductor.

Sure you might also hahe cooling water leaking in, but that will be noticed other places, and is not the reason you are losing vacuum.

Btw... shame on everyone who rated the guest as 'off topic' and jumped on the 'ga' bandwagon for the seemingly obvious but offbase quick response (from someone who otherwise, very often gives very good responses.... )

Flee to me remote elf

Register to Reply
Member

Join Date: Jan 2008
Location: india
Posts: 9
#10
In reply to #5

Re: High Turbine Exhaust Pressure

03/03/2011 12:22 PM

thanks flee... ultimately leakage found in condenser..

__________________
Manoj Kumar Agarwal
Register to Reply
Commentator

Join Date: Feb 2010
Posts: 87
Good Answers: 7
#11
In reply to #10

Re: High Turbine Exhaust Pressure

03/09/2011 2:34 PM

... you are welcome.

Just to clarify for everyone, you are stating that ultimatey, AIR was leaking into the condenser, right?

The heat exchangers are double wall tube in shell design with tell tales, right? This would make it very difficult for cooling water only and not air to be drawn into a leaking condenser..

.but i'll wait for your confirmation.

:-)

Register to Reply
Member

Join Date: Jan 2008
Location: india
Posts: 9
#12
In reply to #11

Re: High Turbine Exhaust Pressure

03/14/2011 3:14 PM

Actually the leakage found in the line which entering into the condenser.. and this line is not the line through which normal condensate flow.. the purpose of that line to drain out each stages of turbine during shutdown. so air ingress was continue through that portion.

__________________
Manoj Kumar Agarwal
Register to Reply
Commentator

Join Date: Feb 2010
Posts: 87
Good Answers: 7
#13
In reply to #12

Re: High Turbine Exhaust Pressure

03/18/2011 11:15 PM

:-)

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: