Emergency Outdoor Lighting Level

12/17/2010 2:51 AM

Hello,

I just need to know what is the emergency OUTDOOR lighting level (in Lux) required by NFPA?

Thank you.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Emergency Outdoor Lighting Level

12/17/2010 8:16 AM

7.9.2 Performance of System.
7.9.2.1 Emergency illumination shall be provided for not less than 1½ hours in the event of failure of normal lighting. Emergency lighting facilities shall be arranged to provide initial illumination that is no less than an average of 1 ft-candle (10.8 lux) and, at any point, not less than 0.1 ft-candle (1.1 lux), measured along the path of egress at floor level. Illumination levels shall be permitted to decline to not less than an average of 0.6 ft-candle (6.5 lux) and, at any point, not less than 0.06 ft-candle (0.65 lux) at the end of the 1½ hours. A maximum-to-minimum illumination uniformity ratio of 40 to 1 shall not be exceeded.
7.9.2.2 New emergency power systems for emergency lighting shall be at least Type 10, Class 1.5, Level 1, in accordance with NFPA 110, Standard for Emergency and Standby Power Systems.
7.9.2.3 The emergency lighting system shall be arranged to provide the required illumination automatically in the event of any interruption of normal lighting due to any of the following: (1) Failure of public utility or other outside electrical power supply. (2) Opening of a circuit breaker or fuse. (3) Manual act(s), including accidental opening of a switch controlling normal lighting facilities.

Reply
Anonymous Poster
#2
In reply to #1

Re: Emergency Outdoor Lighting Level

12/17/2010 8:29 AM

I guess that the 10.8 Lux is related to INDOOR emergency lighting. Does it apply to OUTDOOR lighting as well?

Thanks.

Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3
In reply to #2

Re: Emergency Outdoor Lighting Level

12/17/2010 9:29 AM

You are asking me for an intrepretation of the regulations. I do not posses the proper training or certification to provide such intrepretations.

Perhaps someone else here can.

Reply
Anonymous Poster
#4
In reply to #2

Re: Emergency Outdoor Lighting Level

12/17/2010 1:14 PM

When you are OUTDOOR, no emergency. This standard for ensuring minimum Illuminance level for escaping in emergency situation INDOOR.

Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#5
In reply to #4

Re: Emergency Outdoor Lighting Level

12/17/2010 1:40 PM

Just to play devils advocate, what about an open air (sports) stadium, and, in particular, around stairways. Is that considered indoor or outdoor?

Reply
Anonymous Poster
#6
In reply to #5

Re: Emergency Outdoor Lighting Level

12/17/2010 1:58 PM

only the open to sky play area-ground- is considered OUTDOOR. All other area with roof is INDOOR

Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8
In reply to #4

Re: Emergency Outdoor Lighting Level

06/18/2012 1:06 AM

In outdoors is normal moonlight enough to see clearly escape routes/objects?.

__________________
pnaban
Reply
Participant

Join Date: Jun 2011
Posts: 1
#7

Re: Emergency Outdoor Lighting Level

06/10/2011 9:21 AM

Check out our site and fill out our contact form. We will be glad to give you the information you need. We also have a lot of outdoor lighting products within our department.

Reply