what is the scope of keeing ct links shortened prior to commissioning?
Re: CT short links
12/18/2010 4:25 AM
If the power is applied with the CT output open circuit, the voltage across the CT terminals will rise to a value approx. equal to primary voltage x (current reduction ratio).
e.g. with a 5/1000 CT, ratio is 200:1, so 400V not primary would give 80000V at CT terminals.
Re: CT short links
12/18/2010 5:19 AM
s.b. "400V on primary ..."
Re: CT short links
01/03/2011 5:13 AM
That would make the scope "on every occasion", then?
Re: CT short links
01/03/2011 9:13 AM
Once the CT outputs are safely connected to a shunt resistor, the short can be removed.