Contactor Coil Resistance Values

12/18/2010 11:13 PM

I've looked everywhere. Can someone tell me what are the typical ohm values of coils of contactors. I'm looking for the typical resistance value across a 24vac coil, 120vac coil, 240vac coil and 440 vac coil. Are they approx the same for all manufacturers (square d, GE...)? Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Contactor coil resistance values

12/18/2010 11:25 PM

Yes.

Reply Off Topic (Score 5)
Anonymous Poster
#9
In reply to #1

Re: Contactor coil resistance values

12/19/2010 2:12 PM

Removed by Admin. Inappropriate Content.

Reply Off Topic (Score 5)
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: Contactor coil resistance values

12/19/2010 12:53 AM

No. (Or at least not necessarily.) For instance, a 24v coil on a big relay or contactor will typically have less resistance than such a coil on a small relay or contactor.

That said, it is sometimes hard to find out what the coil characteristics (e.g., va consumed) are, as they tend to be hidden among the miscellaneous data of various catalogs.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Contactor coil resistance values

12/19/2010 1:04 AM

i assume you are aware that the inductance (in open and sealed conditions) is more significant than the resistance in AC coils. Here are the values for one Schneider contactor....

i have not come across such data in GE or other US catalogues. Anyway, i am curious why you need this data...can you please enlighten me? thanks.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Anonymous Poster
#5
In reply to #3

Re: Contactor coil resistance values

12/19/2010 2:26 AM

I started a new job. I'm following someone that is no longer employed in my position. The coil in question controls circuit #1 which is a 3 phase compressor of a package AC unit. The coil control voltage is 240v. On one side of the coil I have 120v. On the other side is the protection side i.e. LP switch, HP switch...which only has 60v. Total voltage drop was about 160v across the coil. I think my predecessor put a 120v coil contactor in to make it work. It finally chattered enough to burn a pad on one of the contactors which single phased the compressor and smoked it. I have the old contactor and it reads about 150 ohms and the replacement is about 350 ohms. The replace was order by PT# off the old one. (I'm going by memory and its be several hours and a couple beers).

Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: Contactor coil resistance values

12/19/2010 3:37 AM

Thanks for the details.

i am not able to understand the 120V, the 60V and the 160V values that you mention... perhaps a single-line diagram would clarify. No matter....i don't think i am in a position to cheer you up. You may need a new contactor, since you say one contact (pad?) burnt and caused single-phasing.All contacts need to replaced in such a case.You may also need to incorporate a single-phase-preventor to avoid future problems. Furthermore, if the compressor motor is refrigerant-cooled, you need a verrrrry good overload relay...since the motor's locked-rotor withstand will be quite low due to the fact that the refrigerant is not moving !

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#4

Re: Contactor coil resistance values

12/19/2010 1:19 AM

Well they will be similar for the same type of task but unfortunately there are so many different amounts of mechanical work that each contactor must do to open and close a particular circuit. There is a good reason that there are so many different types of relays and contactors. At the same time I cannot think of a single contactor I've ever used that had a unique coil resistance.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
2
Associate

Join Date: Nov 2010
Location: Kazakhstan
Posts: 27
Good Answers: 2
#7

Re: Contactor Coil Resistance Values

12/19/2010 12:53 PM

Why you are so confused ?

The answer to your question is very easy if you use your Ohm meter and measure the resistance.

Reply Good Answer (Score 2)
Anonymous Poster
#8
In reply to #7

Re: Contactor Coil Resistance Values

12/19/2010 1:22 PM

Or just check the contactor data sheet.

Reply Score 1 for Good Answer
Power-User

Join Date: Jul 2007
Location: Melbourne Florida
Posts: 122
Good Answers: 2
#10

Re: Contactor Coil Resistance Values

12/21/2010 4:57 PM

If you are trying to troubleshoot this problem, the coil values really don't matter much. You only need to supply enough voltage and current to the coil.

If the reading of 120VAC was from ground to the coil A1 , 60 VAC A2 to Ground on the coil. If this is the case then you have one of two scenarios, 1 either you have a bad connection on the A2 line. or you are supplying 120 VAC to the coil.

In either case you appear to have a bad connection somewhere. Or it is possible the the control transformer is faulty.

Good luck!

__________________
repeat problems can not be solved by the same way of thinking ( A. Einstein)
Reply Score 1 for Good Answer
Reply to Forum Thread 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: