Restricted Earth Fault Relay CT

12/20/2010 11:56 AM

In a restricted earth fault protection relay, where is the best location of 4 CTs, on line side (upstream) of LV main circuit breaker in the secondary of 11 KV delta /415Y 2000 KVA transformer or load side (downstream) of LV main circuit breaker. From terminal of transformer to LV main breaker is 4000a bus duct.

Please note that fault could happen on the bus duct while the transformer is energized with LV main breaker is open

appreciate any suggestion re this problem.

Thanks. rudy_fernando5r

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#1

Re: Restricted Earth Fault Relay CT

12/21/2010 12:00 AM

The ideal location of CTs are in the Transformer LT Terminal box at the tapping point of busduct.

Generally the transformer manufacturer gives the neutral CT before earthing of the neutral,in such case 3 CTs to be installed in the LT terminal box.

The restricted earth fault relay to be made to trip the HT side breaker

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#2

Re: Restricted Earth Fault Relay CT

12/21/2010 2:09 AM

REF only operate for earth fault in protected zone

The location of CT for REF shall be at the end of zone to be protected with REF function. In your case Incoming terminals of LV main Circuit breaker including bus duct.

It is very important to note that the neutral shall be earthed after the CT for REF are installed. In other words, The neutral shall not be eartherd at transformer Neutral bushing but after REF neutral CT.

If Neutral is earthed at transformer and CT are provided at end of Bus duct, the REF would not give any protection and not operate at all.

__________________
When was last time you did something for first time.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: May 2009
Location: Philippines
Posts: 23
#5
In reply to #2

Re: Restricted Earth Fault Relay CT

12/22/2010 12:37 PM

HS,

Thanks for your response. Actually your recommendation to install the CT on the line side of main circuit breaker is according to the restricted earth fault protection relay manufacturer's recommendation.

However, the authority where I currently work in a foreign country, the recommendation is, CT should be on the load side of the breaker.

Best regard,

rudy_fernando5r

Register to Reply
Active Contributor

Join Date: May 2009
Location: Philippines
Posts: 23
#7
In reply to #2

Re: Restricted Earth Fault Relay CT

12/30/2010 9:06 AM

HS,

For the benefit of all CR4 users, it would be a good idea to show in a 3 line diagram (transformer, LV bus duct and LV swithcgear breaker) the location of the 3 phase CTs and the neutral CT.

Thanks and regards,

rudy_fernando5r

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Restricted Earth Fault Relay CT

12/21/2010 3:36 AM

Hmmm, two different answers.

Ramvinod's answer will protect the transformer only.

Happy singh's the transformer and bus-duct.

I'd go for HS's method.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User
India - Member - New Member

Join Date: Jul 2010
Location: India
Posts: 162
#4
In reply to #3

Re: Restricted Earth Fault Relay CT

12/21/2010 4:17 AM

Thanks TonyS,

In plant I worked, we had same arrangement of REF for protection of Transformer and Bus-duct.

__________________
When was last time you did something for first time.
Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#6
In reply to #4

Re: Restricted Earth Fault Relay CT

12/29/2010 5:17 AM

I think the breaker side installation of CT is more common practice which covers Trafo & busduct, the zone coverage is more.

__________________
BNDas
Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

biswanath.das (1); Happy singh (2); ramvinod (1); rudy_fernando5r (2); TonyS (1)