we have installed new 3.3kV FCMA Soft Starter installed for a Zero-Flaring Compressor. Motor is 600kW/3.3kV rated (Full Load-121Amp).
We have tested Zero Flare motor for the first time with both the generator in parallel operation mode and load shading on MCC bus, following are the observations.
1. As per the discussed plan according to operating procedure, initial start was given for 3 sec to verify any abnormalities during instantaneous run. Found normal.
2. Second start was given after 10 mints to check the sequencing of soft starter, measurement of instantaneous current and voltage dip. It was observed that, after 10 sec motor found tripped on Instantaneous over current (IOC) and during this time current was recorded as 350 amps on soft starter and no voltage variation observed on TG control panel. Direction of rotation of motor was found reversed. It was decided to stop the exercise. Motor DOR to be changed.
3. Instantaneous over current (IOC) is set as 700% and instantaneous over current start delay is set as 1 cycle.
SOS- Pls advise what could be reason- should we change the Timer setting?
4. The very purpose of incorporating FCMA starter was to reduce this dip to less than 10% to avoid the tripping of other drives due to this starting voltage dip.
5. Should FCMA starter tap shall be adjusted to different taps and reduce step timer as so that current kick is controlled below 4.8 times??.
6. We observed that the start kick in both the steps of FCMA is going to be around 480%. Also the step timing can be 7 sec depending upon the motor starting condition.
In view of above, to avoid further tripping of locked rotor unit after resolving above problem, should we also recommend to modify the following setting,
|
Item No. |
Program Menu Display |
Existing Setting |
Recommended Setting |
|
17 |
LRC
Locked rotor current in % FLA |
300% |
500% |
Expert opinion is Urgently needed to resolve to see atleast the motor run freely with Compressor de-coupled.
Greatly appreciate this SOS call.