Time Delay of ATS

12/27/2010 3:39 AM

how to make the breaker operating mechanism in millisecond for ats panel when main supply is shutdown.Normally motor spring will take charging time1-5sec.how to reduce transfer time delay. please Could anyone suggest to me to operate at continues load.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: time delay of ats

12/27/2010 4:01 AM

Instead of motor charging of the closing mechanism have a look for solenoid closing ACB's.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Anonymous Poster
#2

Re: time delay of ats

12/27/2010 4:13 AM

wht's breaker ur using .generally breaker colsing is not effected by motor charging

Register to Reply Off Topic (Score 5)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: time delay of ats

12/27/2010 7:13 AM

Does this breaker have an electric release solenoid for the "closing" springs?? This would normally be in a circuit for operation by a "Close" pushbutton. If yes, you could arrange to operate the winding motor, to charge the closing springs, without an immediate close. A "fully open" contact of the "main supply" breaker could be wired to energize that release solenoid. But, maybe you have the simplest possible mechanism - the closing springs are released mechanically as soon as fully wound - the "close" pushbutton operates the motor. Please advise.

Register to Reply
Active Contributor

Join Date: Jul 2010
Posts: 15
#4

Re: Time Delay of ATS

12/28/2010 12:26 AM

This spring charging time shall be allowed for a circuit breaker . Select a spring charging motor of higher capacity. Then the time may come down to 2-3 sec.Is it OK?

The components of the breaker shall be capable of such operation? Relevant International standards shall be referred for this.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#7
In reply to #4

Re: Time Delay of ATS

12/28/2010 2:21 PM

Original Post (Mohamedhajah) wrote "milliseconds". He wants a momentary break, not seconds.

Register to Reply
Anonymous Poster
#5

Re: Time Delay of ATS

12/28/2010 1:36 AM

I am not sure whther it does work on your apllication, but for HVAC industry they use capcitor to store the charge in Damper Actuator. During power the capcitor stores the charge while damper is fullu open. In case of power loss, this capcitor discharges to close the Damper. Earlier version od Damper Actuators use to with Sprin wound which use to release the spring during power loss thus bringing back the Damper Actuator to close position.

You can visit Neptronic Controls from Canad and see how it works. www.neptronic.com

Regards,

M. A. Baig

Register to Reply
Anonymous Poster
#6

Re: Time Delay of ATS

12/28/2010 11:44 AM

Why don't you use ultrasound delay line instead of the motor? It is used for that purpose in every TV receiver.

Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Dec 2010
Location: Brasil
Posts: 21
#8

Re: Time Delay of ATS

12/31/2010 9:09 AM

Hi Mohamedhajah

If you have an ATS you should have a genset, if yes the genset must provide the power to switch the ATS, if wiring and parameters are ok.

If you have no genset, you can change the wiring to mantain the spring loaded, as already written above, and use a low voltage solenoid, this will open the breaker allways the tension goes below a specific value.

Register to Reply