altistart 48

12/30/2010 10:13 AM

Facing problem with altistart 48 soft starter used for 75kw pump application.

starter trips in few second after start up with a fault 'PHF' - loss of line fault. But circuit has been cheked for contactors and relays but everthing smees to be ok.

what could be the possible reason?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Anonymous Poster
#1

Re: altistart 48

12/30/2010 11:17 AM

Annachi, replace the soft starter.

Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: altistart 48

12/31/2010 1:07 AM

It's been a while since I messed with one of those pieces of junk, but I seem to recall that the PHF display means Phase Loss fault. The starter has detected that at least one of the phases is not pulling enough current, which is what would happen if you lost a line fuse. But because the condition can be satisfied if ALL 3 phases are too low, you can get a false trip if the motor is not pulling enough current after a pre-determined (by the factory) amount of time, i.e. 30% of the unit rating by 3 seconds is typical. This happens a lot with pumps unfortunately, because the load does not couple with the motor until the water flows, and it may not flow during the earliest parts of a long ramp.

There are several solutions:

  1. Decrease the ramp time. This happens sometimes because people seem to think a soft starter is like a VFD and they can ramp it for a long time. Not so, especially on centrifugal pumps. Centrifugal pumps must typically be accelerated to 80% speed in no more than 5 seconds total, sometimes even less if they are fluidic bearings.
  2. Disable the Phase Loss protection. In some cases the low acceleration rate cannot be avoided and in order to prevent this false tripping, you must disable the Phase Loss all together. I'm not sure if the ATS48 has it, but on some I would then enable the Phase Imbalance protection in lieu of Phase Loss, it will do the same thing but without the risk of false tripping.
  3. Make sure your soft starter is sized correctly. Some people think that "bigger is better" and buy a soft starter that is much much bigger than necessary for the task. Unfortunately because the Phase Loss trip threshold is based on the UNIT rating, not the motor programmed FLA, you end up with this situation. If so, it will not work (unless maybe you do 1 or 2 above) and must be replaced with a unit closer to the motor size.
__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Anonymous Poster
#3
In reply to #2

Re: altistart 48

12/31/2010 4:34 PM

CR4 ADMIN: Deleted Post

Abuse/Attack: This post was deleted because it was an attack on another user. Please review the CR4 Site FAQ and the CR4 Rules of Conduct.

Register to Reply Off Topic (Score 5)
Participant

Join Date: Aug 2016
Posts: 1
#4

Re: altistart 48

08/23/2016 6:11 AM

We have faced this same problem. We checked all the wiring, the motor, decreased ramp time and double checked all settings. We removed the power board and could see evidence of damage. Replaced the power board and the starter has been running good since.

Register to Reply
Register to Reply 4 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Bradplum (1); JRaef (1)

Previous in Forum: Difference Between 0.2 and 0.25 Accuracy Class Tariff Meter   Next in Forum: Using Three Inverters Instead of One

Advertisement