Using Three Inverters Instead of One

12/30/2010 10:02 PM

Using a three phase induction motor with the following specs; 800 Kw, V = 345, Amps = 565, RPM 85-850-1300.

Starting method through three inverters (Mitsubishi FRN 315 VG7S-4 ).

I am trying to determine the function of three inverters instead of one inverter to drive the motor.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Using Three Inverters Instead of One

12/30/2010 10:26 PM

These numbers look a bit odd; at 345 V, an 800-KW motor ought to draw much more than 565 A.

I'm wondering if the chassis size for the overall inverter is causing it to be made up of three single-phase inverters. [??]

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Using Three Inverters Instead of One

12/31/2010 12:52 AM

That part number is for a Fuji, not Mitsubishi, drive. Each drive is 3 phase, rated 585A, so each drive is capable of running that motor; I guess...

I say "I guess" because I'm not sure why you are showing 3 different RPM ratings. Is it a 3 speed motor? If so, then the nameplate would show 3 separate FLA ratings, one for each speed. I find it hard to believe however that you have a motor that is wound in such a way as to provide those speeds, it makes no sense to me. Something is amiss here, you are leaving out a lot of details, you have related the information incorrectly, or you are making this up to mess with us.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#3
In reply to #2

Re: Using Three Inverters Instead of One

12/31/2010 2:59 AM

Thanks for the reply but be rest assured i am not trying to mess anything. What ever information was passed on to me i have mentioned except that on the schematic electric diagram the motors has 9 leads coming out from motor and connected to the motor terminal box and each one off the inverter is connected to 3 leads i.e. for each inverter there are 3 leads.

Sorry for the wrong information regarding the manufacturer of the inverters.Regarding 3 RPM this is mentioned on the schematic diagram.The name plate has the following data.

fuji electric 3 Phase induction motor, type MSF 9506 A.

800 Kw, Poles 6, Phase 3*3. RPM 850/1300, Hz 42.7/65.4 , Voltage 345/355, Amps 565/525

Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#5
In reply to #3

Re: Using Three Inverters Instead of One

12/31/2010 1:39 PM

Well, it's still confusing but the motor details seem in line with the VFD selection apart from the power. (300kW?)

The 3 speeds seem to be standard rated speeds for a 6 pole so the connection of 3 VFD seems a mystery, are there switches between the VFDs and the motor?

How many terminals inside the motor terminal box, connection diagram and a good application description may help BUT what is the main point of your query or reason to enquire re this whole arrangement?

__________________
Something new every day!
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#6
In reply to #5

Re: Using Three Inverters Instead of One

01/01/2011 3:32 AM

800Kw motor is installed in Aluminum file manufacturing plant in the extruder section.

Extrusion is a process in which solid thermoplastic material is melted and forced through an orfice (Die) of desired shape and then cooled.

The processing steps involved in extrusion are:

  • Feeding
  • Melding
  • Pumping
  • Forming
  • Cooling

I am scanning the schematic diagrams (3No.) hope they will help to find solution to my question.

Register to Reply
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#8
In reply to #6

Re: Using Three Inverters Instead of One

01/02/2011 9:58 AM

The scans are not quite clear to read some relevant information.

it looks like the drives are on the T-link interface so I wonder if they are somehow locked in phase.

Please confirm motor connections from the inverters and also clarify what is fitted at the VFD output terminals UVW, shown in the drawing but can't read - is this a choke/reactor?

Please also confirm your basic query too if possible. One clue may be VG7 only goes to 400kW rating hence the parallel control structure for the larger motor?

__________________
Something new every day!
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Feb 2010
Posts: 164
#9
In reply to #5

Re: Using Three Inverters Instead of One

01/06/2011 5:34 AM

I am re-scanning the inverters drawing (only that portion which can be of help).

Regarding my basic query. My company is carrying out energy audit of the manufacturing plant and to get some technical information from the concerned dept. is hell of a job.

When I came across 800KW, connected through 3inverters my mind struck with the question that what is the use of 3 inverters is it load sharing technique or some other factors are involved. In order to clear my conception I was left with only option to get guidance from CR4 forum.

With your guide line I have come to the conclusion that as you have pointed out, VG7 only goes to 400KW rating, hence to run 800KW with 1.5 S.F (which they disclosed to-day) they need 3 inverters to run the motor.

Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#10
In reply to #9

Re: Using Three Inverters Instead of One

01/06/2011 5:55 AM

OK, glad the information helps.

It looks like the suppressing reactor (ACL 74B) is in circuit as part of this arrangement as I suspected.

__________________
Something new every day!
Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#11
In reply to #9

Re: Using Three Inverters Instead of One

01/06/2011 11:50 AM

Came across something similar using a synchronising module (SIR) to enable the parallel technique using the ACReactor as depicted. In this case the supply was from phase shift transformers (to limit harmonics on the mains supply side, I suppose).

__________________
Something new every day!
Register to Reply Score 1 for Good Answer
Anonymous Poster
#12
In reply to #11

Re: Using Three Inverters Instead of One

01/07/2011 2:33 AM

Received more information from plant which I am passing on to you please comment. 1. Large capacity motor drive The multi – windows system of VG7S is the product applicable to drive the induction motor (hereinafter called motor) with multi-winding coil (hereinafter called multi-winding) from 2 to 6 windings. This allows operation of one motor by sharing load into multiple converts. The maximum capacity of the VG7S units is 800kW. To drive the 1200kW motor, three 400kW inverters or two 630kW inverters are connected. 2. Sensorless vector control. Mulity-winding motor can be sensorless vector controlled. 3. Current sharing To drive one multi-winding motor with multiple inverter, it is necessary to mount the optical link option on each inverter. This optical link instantaneously conveys the current command to share current for each winding. Each inverter control current (feedback control) for each inverter during operation. 4. Minimized wiring Multiple inverters are defined as that one is the master and others are slaves with the switch settings on the option. The master inverter gives operation command and speed command as in a standard product and performs feedback connection (not required for the sensorless type) of the motor encoder. In contract, the function of the slave inverter is to share current. Connection for operation command or speed command is not required wiring is main circuit, alarm output to external unit and optical link. 5. Switching multi-winding motor drive/single (standard) motor drive When each inverter needs to drive an individual motor one to one (hereinafter called single motor drive) after operation of one multi-winding motor with multiple inverters, multi-winding motor drive and single motor drive can be switched with digital input signal. The constants (motor parameters) for three motors can be preset on each inverter. The motor constant (parameters which is used in switching can be switched with digital input signal. Note: I personally thank you for guiding me in the correct direction. Without your sincere guidance I would never been able to get hold of the information mentioned above from the plant management hope in future you will keep on guiding the CR4 forum members.

Register to Reply Score 1 for Good Answer
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#13
In reply to #12

Re: Using Three Inverters Instead of One

01/07/2011 10:04 AM

OK, this is what I found:

Item Explanation
Control method Vector control or Sensor less Vector control
Maximum output frequency 120Hz
Inverter ROM version Standard version (H10062 and H20062 or later) Specially version (H12402 and H22402 or later)
Control option card: OPC-VG7-SI (Option ROM version is Q10017) OPC-VG7-SIR (Option ROM version is Q10050)
The max. number of the parallel connection 2 3 to 6
Motor Induction motor with multi winding coil from 2 to 6

The master inverter is closed loop with encoder, the slaves are open loop connected by the option card to 'share'.

Sounds like someone's regurgitated a generic description rather than your specific application, but I guess you syncronise frequency and control voltage to control the current to a demand level.

Sounds like the application was for 1200kW that was discussed, yours is 800kW - do you have any queries or applications in mind?

__________________
Something new every day!
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Feb 2010
Posts: 164
#14
In reply to #13

Re: Using Three Inverters Instead of One

01/08/2011 11:53 AM

thanks for your e mail in response to my e mail(as mentioned Guest). once again thank you and appreciate your efforts in helping to solve my query.

salahuddin zia

Register to Reply
Participant

Join Date: May 2014
Posts: 1
#15
In reply to #13

Re: Using Three Inverters Instead of One

05/31/2014 10:13 AM

well i had read all the discussion about the said topic

we are facing the same problem in our plant, in plant total three Fuji Electric inverter type FRN315VG7S-4 are installed to run the induction motor Fuji Type MSF9506A. out of these three inverter one is master while other both are Slave.

As the motor contains three windings and for each winding their is a Fuji Inverter.

we had check all the inverters individually and run the motor with no Load (coupling open) and were found normal running with low RPM. But when we connect all the three inverters to run the single motor we get Erb alarm on all the three inverters as the master drive get the signal to start.

Kindly give your expert opinion about the said problem

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Using Three Inverters Instead of One

12/31/2010 12:33 PM

Very odd nameplate information. Google found no reference information on anything I could enter on that motor,must be something custom made. In that case, only the designer of the system can explain why they are using 3 inverters. Very unusual though.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator

Join Date: Nov 2006
Location: Roscoe IL
Posts: 69
#7

Re: Using Three Inverters Instead of One

01/01/2011 3:41 PM

How big of an extrusion press is this? what size billets/container? Is this the main drive motor?

__________________
God's greatest gift is the ability to learn.... and the worst curse is the ability to rationalize our behaviour
Register to Reply
Register to Reply 15 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Bilalkhan (1); duffdr (1); JRaef (2); MalcolmK (5); salahuddin zia (4); Tornado (1)